How to Close ViewX Client Connections
Hello Everyone,
One of the client workstation has opened multiple ViewX sessions and consumed the License. (Different Windows users logged in same computer and opened ViewX sessions and did not close the session).
When we try to login from another workstation we are not able to login due to ViewX license limit.
I am able to see the active ViewX sessions in Status > Server > Clients Tab, along with the IP address of the workstation but I am not able to close or terminate that session.
How can we close the ViewX sessions from DB server.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-1701:28 AM
No direct way apart from stopping the ViewX process.
Consider using Inactivity Logout and then Inactivity Shutdown:
Set them both in the above dialog, AND ALSO set it in Server Configuration:
Note - if you have 'Allow per-user configuration' set, then you have to change the setting in the Security Tab of every user you want it to apply to.
So when a user is logged in, they get (say) 10 min of inactivity and they are logged out. Then the Guest user gets 10 min of inactivity and ViewX is shut down.