Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Getting Template Name or id from an Instance

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: Getting Template Name or id from an Instance
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Spock sbeadle Spock
217
BevanWeiss
Spock BevanWeiss
81
AndrewScott
Captain AndrewScott
54
AdamWoodland
Commander AdamWoodland Commander
23
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: ‎2021-11-23 05:21 PM . Last Modified: ‎2023-05-03 12:00 AM

0 Likes
4
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-11-23 05:21 PM . Last Modified: ‎2023-05-03 12:00 AM

Getting Template Name or id from an Instance

Is it possible to get the corresponding template name or Id of an Instance through the Automation Interface? My goal is to be able to find out if a property is overridden in the template

 

My code snippet is 

 

InstanceFullName = "ParentGroup.InstanceName"

Set obj = server.FindObject(InstanceFullName)

TemplateId = obj.TemplateId

InstanceId = obj.InstanceId

 

I see that TemplateId is always 0 but InstanceId gives me the Id of ParentGroup if ParentGroup is another Template Instance otherwise I get 0

 

Eventually I would like to execute the following method on a few property names 

 

tobj.PropertyOverride(TemplateId, PropertyName) (tobj -> Item inside the template)

Labels
  • Labels:
  • SCADA
  • Scripting
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-11-24 08:15 PM

1 Like
3
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-11-24 08:15 PM

I think you'll probably want the 'ParentTemplateId' property.

 

Which is described as "Reference to the template containing the object, if any."

So if the object has a ParentTemplateId that is not -1 then it is from a template, and you could reference the ID to obtain that template.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: ‎2021-11-29 09:49 AM

In response to BevanWeiss
0 Likes
2
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-11-29 09:49 AM

@BevanWeiss 

 

I don't see a ParentTemplateId method for SCXV6Object. I think you might have referred to the Property ParentTemplateId. I get -1  for both for an independent object( not part of any template) or a template object. I think the reason could be because the object I am checking is inside a template instance. So when I try ParentInstanceId, I get the "Id" of the Parent Group Instance.

 

I think I can work with this idea:

Lets say obj is the object for which I have to check if a property is overridden

1. Get the Parent Instance Id : obj.Property("ParentInstanceId")

2. Find the corresponding Group Object: 

3. Get the Template Id property from the Group Object ( we cant use this on obj because it will fail)

4. Find the Corresponding Template Object ( tObj )

5. Use the Find method under SCXV6Object to see if the Instance Name ( obj.Name ) exists in the template

6. If it exists then use the  PropertyOverride  method:  tObj.PropertyOverride( tpObj.Id, propertyName). This would return either TRUE or FALSE

 

 tpObj would be Nothing if obj.Name doesn't exist in the Template

 

Thanks!!

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-11-29 01:41 PM

In response to tkswathik
0 Likes
1
660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-11-29 01:41 PM


I don't see a ParentTemplateId method for SCXV6Object. I think you might have referred to the Property ParentTemplateId.


Huh?  Wasn't my first sentence exactly this.. "I think you'll probably want the 'ParentTemplateId' property."

 

But yes, my mistake, the ParentTemplateId property applies to tell if a point is within a Template (and which Template), not whether it is within an Instance of a Template.  So it is the 'ParentInstanceId' property you would want.

 

ParentInstanceId should return you the ID of the CTemplateInstance in which your object is located (if it is associated with an instance).

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: ‎2021-11-29 01:51 PM

In response to BevanWeiss
0 Likes
0
657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-11-29 01:51 PM

Ah !! I overlooked it, my bad.

 

Thanks for your suggestion 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc