GeoSCADA to API Gateway

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA to API Gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
115
BevanWeiss
Spock BevanWeiss
98
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2020-01-21 05:21 PM . Last Modified: ‎2023-05-03 12:18 AM

1 Like
5
3659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-21 05:21 PM . Last Modified: ‎2023-05-03 12:18 AM

GeoSCADA to API Gateway

Hi,

reading throuh the GeoSCADA help files I find

 

1.  Introduction to the Simple EcoStruxure Web Services Client Driver, which seems to use a SECWS driver and is programmed directly in GeoSCADA

 

2.  .Net API, Automation Interface and Web Interfaces (SOAP and XML), which seems to require the use of Visual Studio, and adds another component to the communications

 

What is the best method of brining in data to GeoSCADA from an API Gateway?

 

Thanks,

 

 

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-01-23 08:30 AM . Last Modified: ‎2023-04-12 03:06 AM

1 Like
2
3635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-23 08:30 AM . Last Modified: ‎2023-04-12 03:06 AM

Depends on your requirements. The ODBC driver may be useful here for simple data import.

To 'push' data into Internal points you could use the c# .Net API:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Net-API-Automation-Interface-and-Web-Interfaces...

Alternatively you can go all the way and write your own driver with the DDK.

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Driver-Development-Kit-DDK/ba-p/279081

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-02-26 04:41 AM . Last Modified: ‎2023-04-12 03:07 AM

In response to DavidSkilbeck
0 Likes
0
3503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-26 04:41 AM . Last Modified: ‎2023-04-12 03:07 AM

I recommend you go through the DDK guide steps, looking at each aspect of the DDK. You can use the supplied examples (a Modbus scanner) or the Notify driver, and check off each section of the guide as you find it in the code. I'm sure doing it this way will give a working result.

 

Find the PDF guide and installer for the example projects here:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Driver-Development-Kit-DDK/ba-p/279081

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-01-23 08:30 AM . Last Modified: ‎2023-04-12 03:06 AM

1 Like
2
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-23 08:30 AM . Last Modified: ‎2023-04-12 03:06 AM

Depends on your requirements. The ODBC driver may be useful here for simple data import.

To 'push' data into Internal points you could use the c# .Net API:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Net-API-Automation-Interface-and-Web-Interfaces...

Alternatively you can go all the way and write your own driver with the DDK.

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Driver-Development-Kit-DDK/ba-p/279081

Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2020-02-25 01:45 PM

In response to sbeadle
0 Likes
1
3521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-25 01:45 PM

Hi Steve, I built a web client that uses SOAP to GeoSCADA.

There may be better ways. This works and I am not aware of any issues with using SOAP as the solution for that part?

 

I took some time and looked at the DDK and made little progress I'm afraid.

From memory, the code generated a Notify.dll, however there was an issue with the Redirector and 32 / 64 bit references.

(Of course I never had Twilio, though I was only trying to communicate between the Redirector  Web server / client and GeoSCADA).

 

It would be nice to get the driver working and also become more familiar with the parameters used to build the driver.

 

Thanks,

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-02-26 04:41 AM . Last Modified: ‎2023-04-12 03:07 AM

In response to DavidSkilbeck
0 Likes
0
3504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-26 04:41 AM . Last Modified: ‎2023-04-12 03:07 AM

I recommend you go through the DDK guide steps, looking at each aspect of the DDK. You can use the supplied examples (a Modbus scanner) or the Notify driver, and check off each section of the guide as you find it in the code. I'm sure doing it this way will give a working result.

 

Find the PDF guide and installer for the example projects here:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Driver-Development-Kit-DDK/ba-p/279081

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2023-03-16 01:26 PM

0 Likes
0
1955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-16 01:26 PM

I tried to donwload the pdf file, but the link does not exist anymore.  

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-03-17 02:38 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 02:38 AM

The KB has moved since these postings.

Now at: https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Driver-Development-Kit-DDK/ba-p/279081

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.