Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

GeoSCADA OPC UA Client connection with Endpoint (Sign - Basic256)

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA OPC UA Client connection with Endpoint (Sign - Basic256)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Abed
Abed Explorer
Explorer

Posted: ‎2023-04-10 03:26 PM . Last Modified: ‎2023-05-02 11:45 PM

0 Likes
6
2165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-10 03:26 PM . Last Modified: ‎2023-05-02 11:45 PM

GeoSCADA OPC UA Client connection with Endpoint (Sign - Basic256)

I want to use Geo SCADA OPC UA client driver to connect to Prosys OPC UA Simulation server.

I tried to connect with Endpoint (Sign - Basic256). I created client certificate and key using "openssl req" command then imported it to GeoSCADA database but this didn't work for me.

GeoSCADA didn't send the certificate to the Prosys OPC UA Simulation server to trust it. I have manually copied the client certificate into Prosys OPC UA Simulation server trusted certificates and I got the following error in the GeoSCADA OPC UA client driver log file:

(Calling UaSession::UaClientSdk::UaSession::connect
Connecting to the following Endpoint: opc.tcp://MMC-SERVER:53530/OPCUA/SimulationServer
connectError called. clientConnectionId: 0, serviceType: OpenSecureChannel, error: BadUnexpectedError, overridable: false
Connection status changed to ConnectionErrorApiReconnect)

 

Any suggestions? I'm in a critical situation with the client which has a Kepware OPC UA Server with Endpoint (Sign - Basic256) and need to connect our GeoSCADA v84 (October 2022 update) to it using OPC UA client driver.

Labels
  • Labels:
  • Drivers
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
geoffpatton
geoffpatton
Leader

Posted: ‎2023-04-11 11:29 AM

0 Likes
2
2141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-11 11:29 AM

I have not tried anything with OPC UA yet but you might want to just try with Kepware. You can install Kepware and test with it on a development system. It has like a two hour demo runtime. You can just use its default demo database which has simulated IO. After 2 hours you have to stop and start the Kepware service to continue testing with it. Some of their drivers also support putting a device in simulation mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Abed
Abed Explorer
Explorer

Posted: ‎2023-04-12 12:55 AM

In response to geoffpatton
0 Likes
1
2122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 12:55 AM

Thanks!

I'm testing on a simulation OPC UA server and the issue is that Geo SCADA OPC UA client driver didn't send the imported client certificate to the OPC UA Server when connect to the server and then the server refuse our client connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Abed
Abed Explorer
Explorer

Posted: ‎2023-04-12 01:04 AM

0 Likes
0
2122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 01:04 AM

@sbeadle, I have read your post (Creating a Certificate for the Geo SCADA OPC UA Client) and I have created the certificate and imported it to the database but the problem is that when the Endpoint is not None - None then the Geo SCADA OPC UA Client didn't send the certificate to the destination OPC UA Server.

I have tried also Geo SCADA Expert 2022 (v85) but I have the same problem which is that Geo SCADA OPC UA Client is not able to connect to a third party OPC UA Server when the Server Endpoint is not None - None.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2023-04-12 01:40 AM

0 Likes
0
2120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 01:40 AM

While I did post that message, I was not the author and it's not (yet) an area of my expertise!

I hope other users will respond sooner, if not please contact our support team.

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
geoffpatton
Leader

Posted: ‎2023-04-12 06:53 AM

In response to Abed
0 Likes
0
2105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 06:53 AM

I was just thinking that since you said that Kepware is what the customer is actually using you could try it. Maybe it does something a little differently in the connection process and it happens to works.

 

Anyway I hope you get it figured out soon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Abed
Abed Explorer
Explorer

Posted: ‎2023-04-26 08:31 AM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-26 08:31 AM

The solution is published in the following post:

 

https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/OPC-UA-Driver-Setting-Geo-SCADA-2021-Rel-Fe...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore