GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
318
AndrewScott
Admiral AndrewScott
109
BevanWeiss
Spock BevanWeiss
96
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxureโ„ข Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Critcho
Crewman Critcho
Crewman

Posted: โ€Ž2021-02-24 09:27 AM . Last Modified: โ€Ž2023-05-03 12:05 AM

0 Likes
8
3778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 09:27 AM . Last Modified: โ€Ž2023-05-03 12:05 AM

GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

Hi guys,

 

I've set up a test server, using a licence dongle. I tried to set up a DNP3 TCP direct channel, but it was always failed; Quality = Device Failure. When I tried to enable logging on the comms channel per https://tprojects.schneider-electric.com/GeoSCADAHelp/Geo%20SCADA%202020/Default.htm#ServerAdministr..., I noticed that it shows DNP3 as "No License". But my License Details shows DNP3 is enabled. What am I missing here?

 

2021-02-23 GeoSCADA Licence shows DNP enabled but Serve Status shows DNP not licensed - Censored.png

Thanks for your help,

Scott

Labels
  • Labels:
  • DNP3
  • SCADA
  • WITS
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: โ€Ž2021-02-24 12:38 PM

1 Like
7
3772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 12:38 PM

That's usually caused by having unlicensed extensions to the DNP3 driver, if you have them installed and one isn't licensed it takes the whole driver out. Run the installer and check, given you have the core DNP3 and DNP3 WITS you probably have the ENET extension installed but not licensed.

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: โ€Ž2021-02-24 12:38 PM

1 Like
7
3773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 12:38 PM

That's usually caused by having unlicensed extensions to the DNP3 driver, if you have them installed and one isn't licensed it takes the whole driver out. Run the installer and check, given you have the core DNP3 and DNP3 WITS you probably have the ENET extension installed but not licensed.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: โ€Ž2021-02-24 02:48 PM

In response to AdamWoodland
0 Likes
5
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 02:48 PM

As Adam said, WITS, ENET and x70 are potential extensions which aren't the generic DNP3 licence (although ENET and x70 are out of the box licences... I'm think WITS may be an extra costed licence)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: โ€Ž2021-02-24 03:07 PM

In response to BevanWeiss
0 Likes
4
3764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 03:07 PM

What's odd is the screenshot of the licence isn't showing the standard out of the box licence with all the standard drivers included. So wondering if this was something special someone was testing.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: โ€Ž2021-02-24 06:54 PM

In response to AdamWoodland
0 Likes
3
3751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-24 06:54 PM

Ohh right yeah... that dongle licence looks super dodgy.

 

Either it was generated really badly outside of Schneider, or it was very badly generated internally within Schneider.

In the first case, I'd suggest joining a witness protection program and not speaking of this again... in the second case I'd raise it with your Schneider support contact, and get the dongle code re-generated.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: โ€Ž2021-02-25 06:21 AM

In response to BevanWeiss
0 Likes
0
3729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-25 06:21 AM

It could be some specially negotiated low cost minimum licensing.

 

At my previous company we did this with Citect. the licensing would only run as a single server, with Modbus and like 1500 points.

It was supposed to be a easier foot in the door and then get them to upgrade. It was kind of a flop. I only recall a few installations, and they did not grow. very small municipalities.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Critcho
Crewman Critcho
Crewman

Posted: โ€Ž2021-02-25 10:44 AM

In response to AdamWoodland
0 Likes
0
3712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-25 10:44 AM

Thanks @AdamWoodland, looks like that was the issue. I uninstalled DNP3.SCADAPack E (Kept DNP3.WITS), still didn't work. I then went through the installer again, and uninstalled anything that I absolutely didn't need; I'm guessing Schneider Electric SCADAPack x70.DNP3 Protocol was the problem. This must have been installed by default, I have absolutely no need for it, I wouldn't have picked it manually.

 

I know GeoSCADA is a massive system, and this problem is rare, but it could have been handled better, instead of leaving me guessing.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Critcho
Crewman Critcho
Crewman

Posted: โ€Ž2021-02-25 10:44 AM

In response to BevanWeiss
0 Likes
1
3711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-25 10:44 AM

@BevanWeiss there is nothing "dodgy" about the licence, and I'm surprised to see remarks like that on what I thought was a professional forum. It is a cut-down licence specifically generated for suppliers to test their equipment against GeoSCADA using the WITS protocol.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: โ€Ž2021-02-25 02:06 PM

In response to Critcho
0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-02-25 02:06 PM

@Critcho 

dodgy
adjective

 UK informal

  - likely to fail or cause problems

 

Given you were posting to a forum about how the licence is causing you problems, tell me again how this was not dodgy?

 

I would have expected that with such a cut down licence, which is most definitely not 'normal', there would have been some specific use-instructions associated with it.  So when installing a ClearSCADA / Geo SCADA Expert installation you would have had details on exactly which boxes in the installer to tick for this particular licence.

 

All that aside, you get what you pay for.. both in licences, and in forums ๐Ÿ˜‰


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore