GeoSACDA Database Folders, no access permissions as an administrator

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSACDA Database Folders, no access permissions as an administrator
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2020-05-26 08:28 PM . Last Modified: ‎2023-05-03 12:14 AM

0 Likes
5
3599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 08:28 PM . Last Modified: ‎2023-05-03 12:14 AM

GeoSACDA Database Folders, no access permissions as an administrator

I copy customers' database folders so I can have an exact copy to work from for support. This is especially useful if I am using any ID references. I don't copy the History or the Journal. HisFiles and DataFiles only get copied if I have anything in them.

 

I was just making a little program to copy database files into a zip file to make it a little faster process. I just noticed that since I upgraded to GeoSCADA that I cannot access database folders that it creates. any database folders that I have that existed before the upgrade I have full access. I think I was on 2017R2 and skipped 2017R3.

If I create the folders before starting the database then I have access permissions.

 

I know I can force the issue as an administrator but that just a pain in the butt. The Irony is if you access the permissions it shows administrators are the owners and they have full permissions.

 

Does anyone know if this is this something new to how GeoSCADA creates these folders, or coincidently something Microsoft has snuck in on me?

 

I get Everyone does not need to be able to access some folders, but preventing administrators from accessing them I find stupid. You are an administrator, and if a hacker has gotten administrative privileges then they can force access to them anyway.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
tfranklin
Commander tfranklin
Commander

Posted: ‎2020-06-03 06:37 AM . Last Modified: ‎2020-06-03 06:45 AM

In response to sbeadle
0 Likes
2
3559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 06:37 AM . Last Modified: ‎2020-06-03 06:45 AM

I noticed this back in the beta and it appears we can view/modify the files but we have to "grant" ourselves permission first.  I assume this is expected behavior due to how Windows handles permissions.  Is that correct?

 

Workflow:

  • Open the Database folder for the system in question
  • Try opening Config/Data/DataFiles
  • Prompt appears that I need read permissions to view these files, despite me being an admin
  • I can hit continue to continue on and once I do it the first time, I never have to do it again unless I recreate that folder or files within. 

 

So in short, the secondary "confirmation" seems to be more of a Windows process than anything CS related.  Is there anything that can be done to enforce the permissions so that the prompt isn't required provided you have proper permissions?

 

Edit:

 

May have just answered my own question. 

https://support.microsoft.com/en-us/help/950934/when-you-click-continue-for-folder-access-in-windows...

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-05-27 02:05 AM

0 Likes
3
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-27 02:05 AM

From Geo SCADA 2019  the ACLs of  database files should have ACLs added only for the users and groups that should be permitted to modify them (e.g., LocalSystem and Administrators).

See https://www.se.com/ww/en/download/document/SEVD-2019-344-05/

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-05-27 02:22 AM

0 Likes
0
3589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-27 02:22 AM

In Geo SCADA 2019 the "What's New" section of the online help contains a section called "Access Restrictions to Geo SCADA Expert File Locations" which contains more information on the changes to the default access control lists for Windows folders.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
Commander tfranklin
Commander

Posted: ‎2020-06-03 06:37 AM . Last Modified: ‎2020-06-03 06:45 AM

In response to sbeadle
0 Likes
2
3560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 06:37 AM . Last Modified: ‎2020-06-03 06:45 AM

I noticed this back in the beta and it appears we can view/modify the files but we have to "grant" ourselves permission first.  I assume this is expected behavior due to how Windows handles permissions.  Is that correct?

 

Workflow:

  • Open the Database folder for the system in question
  • Try opening Config/Data/DataFiles
  • Prompt appears that I need read permissions to view these files, despite me being an admin
  • I can hit continue to continue on and once I do it the first time, I never have to do it again unless I recreate that folder or files within. 

 

So in short, the secondary "confirmation" seems to be more of a Windows process than anything CS related.  Is there anything that can be done to enforce the permissions so that the prompt isn't required provided you have proper permissions?

 

Edit:

 

May have just answered my own question. 

https://support.microsoft.com/en-us/help/950934/when-you-click-continue-for-folder-access-in-windows...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-06-04 09:17 AM

In response to tfranklin
0 Likes
0
3535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-04 09:17 AM

Well spotted Trent - good find on the ms site. Interesting that Windows spins a bgd proc to assign permissions. 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2020-06-04 09:54 AM

In response to tfranklin
0 Likes
0
3531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-04 09:54 AM

I got off on other stuff but recently I did work on my program some more.

 

I don't have UAC turned on but I still get this prompt, so it is something deeper than UAC, or in Windows 10 and the equivalent Server versions, you can not really turn UAC completely off. Which I am beliving is the case as I also cannot install some custom drivers anymore without also selecting "Run as administrator".

 

I remember this vaguely from the beta now. I was working when I should have just gone to bed.

 

Also, Explorer had gotten off in the weeds somehow because it was not prompting me at all until I launch an Explorer session using "Run as administrator." In the morning I had the bright idea of restarting the computer. That cleared the no prompt issue up.

 

If I use "Run as administrator" on my little program it does get access to the files, if I have not gone through the effort of granting my user permanent access.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore