Geo Scada OPC DA client

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Geo Scada OPC DA client
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2025-12-09 01:47 PM

0 Likes
5
315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-09 01:47 PM

Geo Scada OPC DA client

Hi everyone! I'm trying to read variables using Geo SCADA as a client to an OPC DA server, but I can't even establish a connection. I've tried all the available OPCs in Geo SCADA—OPC Simple, OPC Advanced, OPC XLM-DA, but none of them detect the server. Does anyone have any suggestions?

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-12-09 02:41 PM

0 Likes
1
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-09 02:41 PM

Is the OPC server on the same machine as Geo SCADA or remote?

If remote, are you using a tunnel or directly connecting to the remote IP?

If local, can third party OPC clients connect?

What errors do you get?

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-12-09 09:22 PM . Last Modified: ‎2025-12-09 09:24 PM

0 Likes
1
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-09 09:22 PM . Last Modified: ‎2025-12-09 09:24 PM

There's no point trying to use OPC XML-DA if your server is only OPC-DA.  OPC XML-DA is an entirely different 'protocol' than OPC-DA...

Your issue is almost certainly going to be DCOM security related.  Especially if you're using an up to date operating system on the OPC-DA Server end.

 

If you can change your OPC-DA server over for OPC-UA things will be so very much easier.

Likewise if you can change your OPC-DA server over for OPC XML-DA.. both of these avoid DCOM, and you do really want to avoid DCOM.

 

If you're really stuck with OPC-DA, then you're going to want to start looking up on DCOM, and DCOM security.

To browse for the remote OPC-DA server, you will need to allow for remote start and access to OpcEnum on the remote machine.  If both OPC-DA server and client are on the same domain, then you can use domain authentication, and configure the DCOM authorization based on this.  If they're not... then things start to get much sketchier... sometimes it works if you create a local user on the OPC-DA server, give that permissions for OpcEnum and the server that you need to expose, and then make sure that the OPC-DA client passes through a username/password for authentication.

Often I just end up opening up OpcEnum to anonymous users.. which is terrible from a security perspective.

 

Really really really try to get OPC-UA instead.  It's really so much easier.

Ohh.. or you can try either KepWare / Matrikon OPC Tunnellers

https://www.opcturkey.com/uploads/kepserverex-opc-tunnel.pdf

https://www.matrikonopc.com/opc-ua/products/opc-ua-tunneller.aspx


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2025-12-10 08:04 AM

In response to AdamWoodlandToo
0 Likes
0
289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-10 08:04 AM

Hi Adam, about your questions:

1. the server is remote

2. I'm connecting directly by IP addressing

3. I tested a local connection using a third party opc client and it worked good.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2025-12-10 08:09 AM

In response to BevanWeiss
0 Likes
0
289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-10 08:09 AM

Hi Bevan, thank you for your answer, but unfortunately I'm stuck with OPC DA server.  I'll check the information in the links you sent me.

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-12-10 04:53 PM . Last Modified: ‎2025-12-10 04:55 PM

0 Likes
0
280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-10 04:53 PM . Last Modified: ‎2025-12-10 04:55 PM

Then what Bevan says about DCOM is likely your hurdle and has been since WinXP SP2... follow his suggestions and see what you can get sorted

 

Side note, if the remote server is also ClearSCADA/Geo SCADA, configuring ViewX also sets up a tunnel bypassing the headache of DCOM. If you configure ViewX at the client machine to connect to the remote server (hide it from ViewX if you want) and then point your OPC client to 127.0.0.1

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore