Geo SCADA to S7-1500

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Geo SCADA to S7-1500
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Anag
Crewman Anag
Crewman

Posted: ‎2023-07-26 06:19 PM

0 Likes
3
1897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-26 06:19 PM

Geo SCADA to S7-1500

Hello everyone,

 

We are planning for a Geo SCADA system that will have some Siemens S7-1500 PLCs, and I'm wondering what will be the better option to monitor and control these PLCs; is it Geo SCADA Siemens S7 driver or OPC UA? and what are the advantages/disadvantages of each?

I know that with Siemens S7 driver, the documentation doesn't mention support for S7-1500 but I know it can be done with unoptimised block access and using absolute addresses, which might be a disadvantage. But are there any advantages using this driver than using OPC UA?

 

Labels
  • Labels:
  • Drivers
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2023-07-26 08:34 PM

0 Likes
0
1887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-26 08:34 PM

The OPC-UA usage within S7-1500 does require a license for each PLC.  It's not an expensive license, but it's a factor.

The OPC-UA protocol itself is also 'heavier' than S7Comm protocol.

I don't believe that the GeoSCADA Expert driver supports S7Plus protocol (symbolic for the optimized DBs on S7-1200/1500).

 

Unoptimized DBs also have a 64kB size limit, which doesn't apply to Optimized DBs.

 

It will depend on what you ultimately need.  If you have big DBs, OPC-UA might be your only option for GeoSCADA Expert.  If you just have a small bit of data that you can marshal through an Unoptimized DB, then I'd probably go that way.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2023-07-26 08:34 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-26 08:34 PM

The OPC-UA usage within S7-1500 does require a license for each PLC.  It's not an expensive license, but it's a factor.

The OPC-UA protocol itself is also 'heavier' than S7Comm protocol.

I don't believe that the GeoSCADA Expert driver supports S7Plus protocol (symbolic for the optimized DBs on S7-1200/1500).

 

Unoptimized DBs also have a 64kB size limit, which doesn't apply to Optimized DBs.

 

It will depend on what you ultimately need.  If you have big DBs, OPC-UA might be your only option for GeoSCADA Expert.  If you just have a small bit of data that you can marshal through an Unoptimized DB, then I'd probably go that way.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-07-28 07:46 AM

0 Likes
1
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-28 07:46 AM

@BevanWeiss Does the driver even work for the 1500? It was not clearly answered in this post about a 1200.

https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/Simatic-s7-driver-with-PLC-1200/m-p/438024?...

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2023-08-17 04:20 AM

In response to geoffpatton
0 Likes
0
1699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-17 04:20 AM

@geoffpatton if you're targeting Unoptimized DBs, then an S7-1500 is identical in behaviour to an S7-300/S7-400.  So no issues there.
It's just around the Optimized DBs that the problem arises (i.e. if you want to use fancier data types, or >64kB of data per DB).  Then you can either go the Siemens S7-1500 OPC-UA server, or a third party OPC (DA/XML/UA) server that talks S7Plus.
I don't think GeoSCADA's Siemens S7 driver will support Optimized DB access anytime soon.  It's a pretty locked down (proprietary) protocol, and not particularly well supported in other SCADA platforms either.  I'm currently using Wonderware Intouch that supports it in the SIDirect driver.  But we've had lots of bugs with the PLC<->Visualisation end-to-end that seem Optimized DB / S7Plus specific.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of