GEO SCADA SMS modem

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GEO SCADA SMS modem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
sspurway
Crewman sspurway
Crewman

Posted: ‎2023-02-06 12:41 AM . Last Modified: ‎2023-05-02 11:49 PM

0 Likes
8
3053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-06 12:41 AM . Last Modified: ‎2023-05-02 11:49 PM

GEO SCADA SMS modem

Can anyone recommend a suitable SMS modem that will work with Schneider Electric - Geo SCADA Expert Help - Pager Driver Guide - SMS - Short Message Service (Intro....

 

My preference would be for a SMS modem that supports AT commands over TCP/IP so I don't have to use a serial connection to from the server to the SMS modem as the GEO SCADA server will be virtual also I would not like a to use a moxa serial converter such as a MOXA Nport 5110A as I would like it all in one unit.

 

Regards


Scott

Labels
  • Labels:
  • Drivers
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
LaurentC
LaurentC Cadet
Cadet

Posted: ‎2023-02-21 05:28 AM

0 Likes
0
2974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-21 05:28 AM

I tested the Thales (formely Gemalto) EHS6T LAN on a Geoscada successfully.  It gets the commands on the TCP/IP port 1234.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2023-03-11 09:28 PM

0 Likes
2
2955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-11 09:28 PM

I've used Robustel and Teltonika modems with success as SMS sending.

I can't recall if the Teltonika worked for receiving as well, but after some jiggling (documented somewhere on this forum) I did get the Robustel working for this.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

PBOT
PBOT
Cadet

Posted: ‎2024-07-02 06:04 PM

In response to BevanWeiss
0 Likes
1
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 06:04 PM

@BevanWeiss What was the model of the Teltonika modem you used? did it ever worked for receiving SMS messages?

The Robustel modem, do you know what was the model number?

Thank you 

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2024-07-03 08:36 PM

In response to PBOT
0 Likes
0
2345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 08:36 PM

Never tried on the Teltonika.  For the Robustel, you should search this forum.  The details are available.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Praetoriate
Crewman Praetoriate
Crewman

Posted: ‎2024-11-20 10:25 AM

0 Likes
0
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-20 10:25 AM

Apologies for reviving a resolved post, but I have not had any luck getting SMS (Verizon) working on either a Teltonika RUT241 or a Multitech MTR-LNA7. Out of the box, I cannot find much info on what port AT commands are received on for either and the only SMS settings I can find for the Multitech are for Win911 which seems to operate on telnet. Teltonika support so far does not seem to be familiar with anything remotely close to this application and things some type of custom script is needed to get it working. Any help or direction on configurations would be appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-11-22 03:29 AM

0 Likes
1
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 03:29 AM

Teltonika RUT241

The following page indicates the an SSH client is required to logon to the router and then used to send AT commands to the modem:

https://wiki.teltonika-networks.com/view/AT_Commands 

The Geo SCADA pager driver does not include an SSH client.

 

Multitech MTR-LNA7

The documentation is unclear, but it doesn't appear this router contains a Telnet server (or similar) which can be used to sent AT commands to the modem via the network.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-02-11 09:02 PM

In response to AndrewScott
0 Likes
0
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 09:02 PM


@AndrewScott wrote:

Teltonika RUT241

The following page indicates the an SSH client is required to logon to the router and then used to send AT commands to the modem:

https://wiki.teltonika-networks.com/view/AT_Commands 

The Geo SCADA pager driver does not include an SSH client.


The RUT devices can be configured for Telnet, but it's not enabled by default (security concerns).

https://community.teltonika.lt/t/rut240-as-a-sms-gateway-trough-telnet/4850/3

 

Given the Telnet enables full device configuration, and all the commands need to be funnelled through the gsmctl application (and escaped for use of quotes) it's a bit tricky, and I probably wouldn't recommend their usage.

I'd still recommend the Robustel units (although it's been a couple of years since I last commissioned one).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Higginbotham
Crewman Higginbotham
Crewman

Posted: ‎2025-04-10 12:18 PM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-10 12:18 PM

I tried using the notify driver with a SCADADroid Text modem but it could not reliable send the sms if there were more than 3 or 4 going out at the same time. I ended up using an SMS Eagle and sending the alarms as an email to the SMS Eagle which would send as sms if it is ment to be a text or forward emails if needed. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore