Hi,
I want to know If for a Objet with Group and variation with a 32-bit, I need to assign two continuous addresses DNP3
Example
I have to object:
I have the object Obj_1 type g30V5 32-bits Floating Point Analog Input with Flags and I assign the DNP3 address 1200
For the second Object Bbj_2 type g30V5 32-bits Floating Point Analog Input with Flags, Do I need to assign the DNP3 address 1202 or I can use the 1201 DNP3 address?
Thank you,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-29 01:37 AM
DNP3 addressing is not affected by the variation that is being used to read/write the object. It makes no difference whether the analog input variation is 16-bit, 32-bit or 64-bit.
In your example, the second object should have address 1201.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-29 01:37 AM
DNP3 addressing is not affected by the variation that is being used to read/write the object. It makes no difference whether the analog input variation is 16-bit, 32-bit or 64-bit.
In your example, the second object should have address 1201.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-29 01:43 PM
Hi Andrew,
thanks for the answer