Hello Everyone,
Our client working on Geo SCADA 2021 that the CrystalReport's Driver stopped suddenly.
The events log registered:
| Generate report request rejected - Driver 'Crystal Reports' is not running |
and we've checked the drive log and we've noticed:
(It say username or password is wrong)
However, the odbc(32bit - 64bit) defined with correct logon data
the user was registered as logon as service
We've restart the module/server and nothing worked
Appreciate any hints or solution
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-17 02:13 AM
This error indicates that the credentials for server-side printing (and report exporting) are invalid, see System Administration > Server Administration > Printer Settings so the driver cannot logon to Windows.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-17 02:13 AM
This error indicates that the credentials for server-side printing (and report exporting) are invalid, see System Administration > Server Administration > Printer Settings so the driver cannot logon to Windows.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-17 03:07 AM
Thanks alot
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.