Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-06 02:17 PM . Last Modified: 2023-05-02 11:45 PM
Hey fellows.
I need a hand with some Crystal report export timed out issue. Did anybody experience this before:
I have attached the Event and logs for reference.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-06 02:35 PM
Ok i am good now.
So in the beginning the issue was with the SMTP server in the Server configuration. After i got it fixed the problem stayed the same. I just randomly restarted the Crystal Report driver and it starts working fine.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-12 01:39 AM
Driver's read their settings at start-up, so changes to settings in the Server Configuration Tool that affect drivers don't come into affect until the next time the driver(s) is started.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.