Hi,
When I create a text box in any mimic in Geo SCADA Expert 2021, I can assign any signal from the "Animations-Value" screen and this feature works without any problems. For example, in this image, I can write the WLM_ID value of the signal in the text box I created, and when I change the WLM_ID, the text box also changes.
But what I need is the opposite of that. When I change the value in the text box, I want the WLM_ID in the Identification tab in the signal to be changed. Is this possible?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-12 08:21 AM
You would need to add a script pick action to the text box in the mimic.
The script itself will need to display a form to prompt the user to enter the new value and then write that value to the database field (WLM_ID) of the required database object.
See Mimic Scripts in the help for details.