Communication issues with Geo SCADA in virtual machine

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Communication issues with Geo SCADA in virtual machine
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
96
BevanWeiss
Spock BevanWeiss
90
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
jorge.florez
Ensign jorge.florez Ensign
Ensign

Posted: ‎2025-03-25 09:10 AM

0 Likes
4
317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 09:10 AM

Communication issues with Geo SCADA in virtual machine

Hi:

We have an application with two physical redundant servers. Every server has one virtual machine in which Geo SCADA is installed. One virtual machine is the primary server and the other virtual machine is the secondary server. Geo SCADA clients are installed in other virtual machines inside the physical servers. The virtualization software we are using is Hyper-V.

The application is communicating with several field devices (PLCs) by Ethernet/IP and OPC UA protocols. We started communicating one device of OPC without having any issues but as we connect more than three devices we started to experience communication problems. In Ethernet/IP we have issues since we activated the first device. The status screen for Ethernet/IP shows messages such as: "Communications state-failed-alarm raised", "Lost comm with outstation on channel XXXX". For OPC UA it shows messages such as: "Connection state failed (the operation timed out.)-Alarm raised", "Connection state-Disconnected (Driver failed)-Alarm raised", "Connection state-Disconnected (Driver failed)-Alarm raised", Connection state-Failed (Connection Error API Reconnect)-Alarma raised". In all cases, for both protocols, after approximately one minute the alarm is cleared and the whole process begins again.

We have tested with Geo SCADA installed in a laptop connected to the network and we do not have any problems. That's the reason why we suspect that the problem may have something to do with the virtualization process.

Have you had any reports about similar problems with Geo SCADA installed in virtualized environments?

Do you know about special configurations in virtual machines to help Geo SCADA work properly?

Thanks in advance for any help someone can provide me.

Attachments
Labels
  • Labels:
  • Drivers
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jorge.florez
Ensign jorge.florez Ensign
Ensign

Posted: ‎2025-03-26 06:52 AM

1 Like
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-26 06:52 AM

Hi guys: All of you have part of the solution. Last night I realized that I have a configuration problem with two redundant switches that communicate the physical servers with the devices in the field. I tested unplugging one of the switches and the problem disappeared, so I could inferred that the root and backup configuration were not working properly. Thank you very much for replying so soon. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2025-03-25 12:04 PM

0 Likes
0
298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 12:04 PM

My customers have not noticed any problems like this with VMware. One customer did use Hyper-V, installed a couple years ago and that worked fine. I think they have one server with only one Geo SCADA server VM, and the other had a VM for Geo SCADA server and a VM for Virtual ViewX. they had one big local controller and like 8 small remote sites all using DNP3 but they were polling them like it was Modbus since they had the network bandwidth to do so.

You may have a network bandwidth allocation problem.

I don't know anything about Hyper-V myself but if there are any network bandwidth settings you might want to try adjusting those and give the Geo SCADA Server one the most.

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-03-25 10:21 PM . Last Modified: ‎2025-03-25 10:22 PM

0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 10:21 PM . Last Modified: ‎2025-03-25 10:22 PM

What version of Windows are you running? If not a server OS you might be suffering from the OS throttling your outbound sockets (something Microsoft added back in a service pack of Windows XP to deal with the Internet worms and has caused performance issues similar to this before but not seen this behaviour in a long time so maybe no longer in Windows!)

 

What is your netstat showing for those failing connections? May show where in the TCP lifecycle it is failing.

 

It is possible some security software on the VM or the host is throttling sockets too.

 

I've not seen anything specifically related to performance in virtualisation. You have to make sure the various resources are available and the host isn't having to deal with some over-allocation. Resource over-allocation or dynamic resource assignment can cause issues although that is typically seen on user experience (mimic load times, etc) rather than protocol performance.

 

> That's the reason why we suspect that the problem may have something to do with the virtualization process

 

Sounds like you P2Ved the machine from a physical box, or have I misunderstood and this is a fresh install that has always been virtual?

 

May be worth running some performance benchmarks (with Geo SCADA stopped) to check out the machine's performance in general

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-03-25 10:56 PM . Last Modified: ‎2025-03-25 10:57 PM

0 Likes
0
273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 10:56 PM . Last Modified: ‎2025-03-25 10:57 PM

Assuming none of my comment helps, you might need to do some packet capturing and seeing if the problem is on the packets going out or the packets coming in (if they ever do) using something like Wireshark or the inbuilt Windows features.

 

Channel logging within Geo SCADA could also be an option if that is easier, and you can check the raw txt file for the tx and rx messages or run that file through the driver translator but then you won't see any TCP flags that you'd get with Wireshark which might indicate a low-level problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

jorge.florez
Ensign jorge.florez Ensign
Ensign

Posted: ‎2025-03-26 06:52 AM

1 Like
0
244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-26 06:52 AM

Hi guys: All of you have part of the solution. Last night I realized that I have a configuration problem with two redundant switches that communicate the physical servers with the devices in the field. I tested unplugging one of the switches and the problem disappeared, so I could inferred that the root and backup configuration were not working properly. Thank you very much for replying so soon. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of