Can't Reset Super User Password

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Can't Reset Super User Password
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
MikeSI
Ensign MikeSI
Ensign

Posted: ‎2024-12-04 05:07 AM

0 Likes
6
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 05:07 AM

Can't Reset Super User Password

Hi All,

 

I have inherited a Hot-Standby redundant Geo SCADA server pair running version 2021 (August 2022 update).

Both servers supposedly have a super user account but the login doesn't work. The password can not be obtained.

 

I have tried following the procedure in: https://www.se.com/au/en/faqs/FAQ000244794/ 

to reset the SU password but it hasn't worked. I have tried it on each server separately, plus both servers together.

Normally I would say it's not an issue because an Admin account is available, but in this case the User  and User Group objects in the database are hidden from everyone except the SU. Don't ask me why - I can't see any reason to do this.

This means I can't add users to a group and I can't change passwords for existing users because even as Admin I can't see any of them in the DB tree.

 

Has anyone else had issues with resetting the SU password? Am I missing a step?

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-12-15 05:56 PM

0 Likes
0
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-15 05:56 PM

If it were me I would:

 

  1. Shutdown the Geo SCADA service on the target server
  2. Delete the Reg key at HKEY_LOCAL_MACHINE\SOFTWARE\Schneider Electric\ClearSCADA\DB\WebSSLHash (export the key first or copy the text as necessary)
  3. Run the installer again as you did above and tick the Reset Super User box, enter the details and allow it to complete
  4. Verify in Regedit that the WebSSLHash value is back and has a load of text in (if not then the installer didn't do its job, not aware of anything that would do this but let's double check the installer bit worked)
  5. Create a new system in Configure Connections that only connects to 127.0.0.1
  6. Start the Geo SCADA server on that server and run ViewX
  7. Try to log into that newly created system only (no other system) as the superuser

 

That should hopefully let you in as it should mean you've verified that new superuser details have been written to the Registry and you're only connecting to the local server (as the superuser won't work over the network).

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
tfranklin
Commander tfranklin
Commander

Posted: ‎2024-12-05 06:16 AM

0 Likes
0
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 06:16 AM

If you've stepped through the steps in the link, I'd expect it to work as well.  I've never personally had this issue.  Are you logging in locally to the local DB? Keep in mind SU only works when you're RDP'd in to the server in question.  Outside of that, I can't recall if changing SU requires a restart of the DB, but maybe that's the next thing to check. 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2024-12-05 09:42 AM

0 Likes
1
1721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 09:42 AM

On each server you can run the installer again, select Modify the installation, and select Change super user.

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2024-12-05 09:58 AM

In response to geoffpatton
0 Likes
0
1721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 09:58 AM

LOL it would help if I looked at the link you shared first before posting.

You could try uninstalling and reinstalling I have had to do that for some license server service problems before.

 

Another alternative, if you know your system well enough and know that doing this will not affect any of your processes, you can install Geo SCADA on a computer and set a super user on it. Copy the folders and files from one of the servers' Database folder over to this computer and edit the database to give your admin users permissions on everything. then copy the config folder back. You don't want to copy the history folders or Event Journal folders. You would have to stop both servers while you copy the Config folder back to a server and start and if it is successful then start the other server. other wise stop the server and then start the one you did not update and then start the one you changed and it will retrieve to or files from the running server.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-12-06 12:51 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-06 12:51 AM

In answer to Trent's query, you do need to restart Geo SCADA after changing the SU password.

Don't forget to make a 'real' user the admin and then disable the SU password in the Server Config tool. (The Server Status tool has a warning to encourage you to do this).

Other notes - you can't transfer the SU user/password settings to another server by copying the registry.

Reply

Link copied. Please paste this link to share this article on your social media post.

MikeSI
Ensign MikeSI
Ensign

Posted: ‎2024-12-12 10:45 PM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 10:45 PM

Apologies everyone for such a late reply and thanks for all the responses, I'm away on annual leave and haven't tried to reset the SU again.

It does sound like I've been doing the right thing so a bit of a mystery.

I RDP to the server, shutdown GeoSCADA and run the installer, select modify, and tick 'reset SU' and follow the prompts. Everything appears to work except when I go to login and username/pwd is not recognised.

It will probably be atleast another week until I have a chance to try again.

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-12-15 05:56 PM

0 Likes
0
1579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-15 05:56 PM

If it were me I would:

 

  1. Shutdown the Geo SCADA service on the target server
  2. Delete the Reg key at HKEY_LOCAL_MACHINE\SOFTWARE\Schneider Electric\ClearSCADA\DB\WebSSLHash (export the key first or copy the text as necessary)
  3. Run the installer again as you did above and tick the Reset Super User box, enter the details and allow it to complete
  4. Verify in Regedit that the WebSSLHash value is back and has a load of text in (if not then the installer didn't do its job, not aware of anything that would do this but let's double check the installer bit worked)
  5. Create a new system in Configure Connections that only connects to 127.0.0.1
  6. Start the Geo SCADA server on that server and run ViewX
  7. Try to log into that newly created system only (no other system) as the superuser

 

That should hopefully let you in as it should mean you've verified that new superuser details have been written to the Registry and you're only connecting to the local server (as the superuser won't work over the network).

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore