Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Call built-in Interval Control as a user Pick Action

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Call built-in Interval Control as a user Pick Action
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
rlao
rlao
Contributor

Posted: ‎2020-01-14 10:20 PM . Last Modified: ‎2023-05-03 12:19 AM

0 Likes
4
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-14 10:20 PM . Last Modified: ‎2023-05-03 12:19 AM

Call built-in Interval Control as a user Pick Action

Hi,

 

When configuring fields such as alarm redirection delays and execution offsets (time-based interval properties) in a database object's properties, it brings up a nice Interval control popup that lets you explicitly specify number of hours, minutes, seconds, etc. which makes configuration very intuitive.

 

However, when you call a control method on those types of properties as a pick action for example, you don't get that nice interval control popup. You just get a generic control dialog box and you are forced to input your desired interval as number of seconds.

 

Is there a way to call that nice Interval control as a user method so I can put it into a mimic script?

Labels
  • Labels:
  • SCADA
  • Telemetry
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
BevanWeiss
Champion

Posted: ‎2020-01-15 10:47 PM

0 Likes
3
3230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-15 10:47 PM

There is no way that I know of to do this.

 

In the past we've always had to create a VB form to allow for such 'complex' data entry.

It might warrant a feature request however.  I'm just not sure how it could be exposed.  The ?Control action really attaches to an entire point object.  I guess there could possibly be a ?Configure:'PropertyName' action exposed which would call up the appropriate custom dialog for the PropertyName specified.  Aggregates could be handled with

?Configure:'AggregateName.PropertyName'

 

But again, I don't believe anything like this is currently available within ClearSCADA.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BevanWeiss
BevanWeiss
Champion

Posted: ‎2020-01-15 10:47 PM

0 Likes
3
3231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-15 10:47 PM

There is no way that I know of to do this.

 

In the past we've always had to create a VB form to allow for such 'complex' data entry.

It might warrant a feature request however.  I'm just not sure how it could be exposed.  The ?Control action really attaches to an entire point object.  I guess there could possibly be a ?Configure:'PropertyName' action exposed which would call up the appropriate custom dialog for the PropertyName specified.  Aggregates could be handled with

?Configure:'AggregateName.PropertyName'

 

But again, I don't believe anything like this is currently available within ClearSCADA.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
BevanWeiss
Champion

Posted: ‎2020-01-15 11:01 PM

In response to BevanWeiss
0 Likes
1
3228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-15 11:01 PM

Immediately after I posted the reply I thought of a way that 'might' have worked.  But I just tested it and it didn't.  So you can strike out this option.

 

If you call a Logic Program which has VAR_INPUT parameters configured, put don't specify them when executing (through a UI control), it will prompt you to enter the parameter value.  I was hoping that having a TIME VAR_INPUT it would prompt in a fashion that allowed for entering of time duration, which could then be scaled into the appropriate property value.  Unfortunately this was not the case, and it only provided a simple text entry field (which I'll raise a feature request to try to enhance).

 

So there's no working option I can recommend sorry.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
tfranklin
Leader

Posted: ‎2020-01-16 05:53 AM

In response to BevanWeiss
0 Likes
0
3221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-16 05:53 AM

We've requested this feature a number if times in the past.  My first thought was to have them utilize the DisplayObjectMenu function call and add an option for something like &ControlOnly=TRUE to the end.  DisplayObjectMenu accesses the entirety of the object similar to the ?Control function would. 

 

We've tried using DisplayObjectMenu and excluding everything but control, but since there are other items in that "Group" of exclusions it ultimately still prompts you to select something prior to getting the control menu. 

 

To those who roam the forums about, please consider this feature in future releases.  As Bevan mentioned, the only suitable workaround is to script a form that is somewhat complex due to consideration of varying datatypes and error handling with control min/max. 

  • Tags:
  • control
  • forms
  • pick action
Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
rlao
Contributor

Posted: ‎2020-01-16 03:15 PM

In response to BevanWeiss
0 Likes
0
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-16 03:15 PM

Thanks bevan, I feared this might have been the case. Looks like I'll just have to script a user form myself

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore