Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

CDBEventJournal Custom fields : CustomStringField , CustomNumericField1 ..

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: CDBEventJournal Custom fields : CustomStringField , CustomNumericField1 ..
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-07-10 08:04 AM . Last Modified: ‎2023-05-03 12:13 AM

0 Likes
4
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-10 08:04 AM . Last Modified: ‎2023-05-03 12:13 AM

CDBEventJournal Custom fields : CustomStringField , CustomNumericField1 ..

Hello, how can I allow the update/write of these columns?  They seem to be there for our use however I can't update these columns via QueryPad or via ST script.

 

No hits on searching Help and didn't see anything in Configuration to allow these to be used.

 

thanks

Labels
  • Labels:
  • Logic
  • Tags:
  • CDBEventJournal
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-07-10 11:10 AM

0 Likes
2
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-10 11:10 AM

There fields can only be set programmatically using the following methods:

  • CEventJournal::SetCustomStringField( RecordId, Index, Value )
  • CEventJournal::SetCustomNumericField( RecordId, Index, Value )
  • CEventJournal::SetCustomFields( RecordId, StringValue, NumericValue1, NumericValue2, NumericValue3 )

 

The CEventJournal database table is an aggregate. The aggregate is a field called EventJournal and is on the root group object in the database.

 

The following JScript examples show there use from a mimic script:

 

function SetCustomString()
{
  Server.RootObject.Interface.EventJournal.SetCustomStringField( "0000000001CD5EEAFBCE1E40000001C100000000", 0, "Hello");
}


function SetCustomFields()
{
  Server.RootObject.Interface.EventJournal.SetCustomFields( "0000000001CD6BEB2D16B9DC000054C100000000", "Hello world", 1, 2, 3 );
}

 

The RecordId will obviously need to match an actual record in your event journal and therefore won't be a constant like these examples.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2020-07-10 11:10 AM

0 Likes
2
2225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-10 11:10 AM

There fields can only be set programmatically using the following methods:

  • CEventJournal::SetCustomStringField( RecordId, Index, Value )
  • CEventJournal::SetCustomNumericField( RecordId, Index, Value )
  • CEventJournal::SetCustomFields( RecordId, StringValue, NumericValue1, NumericValue2, NumericValue3 )

 

The CEventJournal database table is an aggregate. The aggregate is a field called EventJournal and is on the root group object in the database.

 

The following JScript examples show there use from a mimic script:

 

function SetCustomString()
{
  Server.RootObject.Interface.EventJournal.SetCustomStringField( "0000000001CD5EEAFBCE1E40000001C100000000", 0, "Hello");
}


function SetCustomFields()
{
  Server.RootObject.Interface.EventJournal.SetCustomFields( "0000000001CD6BEB2D16B9DC000054C100000000", "Hello world", 1, 2, 3 );
}

 

The RecordId will obviously need to match an actual record in your event journal and therefore won't be a constant like these examples.


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-10 09:00 PM

In response to AndrewScott
0 Likes
0
2218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-10 09:00 PM

@AndrewScott For very restricted examples it would be possible to do this using a User Method.

Not sure what the use would be since the RecordId couldn't be dynamically entered... but it would arguably be possible.

 

It's probably important to note that these methods do require Control permissions on the $Root object.

Which for many databases may not be configured for the majority of users.

 

I'm actually intrigued by what permissions are required for the 'AddComment' method on the same aggregate.

It doesn't appear to have a Privilege associated with it in my version (GeoSCADA 2019 May 2020 Update).

2020-07-11 13_58_29-CEventJournal - Internet Explorer.png

 

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-13 11:10 AM

In response to AndrewScott
0 Likes
0
2207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-13 11:10 AM

Thanks for your reply, hadn't seen these methods.  Much appreciated..

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mayghledimo
mayghledimo
Cadet

Posted: ‎2025-08-24 04:14 PM

1 Like
0
334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-24 04:14 PM

For anyone looking for ST syntax. Below is an example program on how to set event log custom string field in Structured Text Logic:

PROGRAM NewStructuredTextProgram
	METHOD
		SetCustomString AT %M($Root.EventJournal.SetCustomStringField):STRING, DINT, STRING;
	END_METHOD
	VAR
		recordid:STRING;
		stringvalue:STRING;
	END_VAR
		
	recordid := '0002A01E01DC10EA27089E9801DC10DBFBBAED1700000000';
	stringvalue := 'change 1';

	SetCustomString( recordid, 0, stringvalue);
END_PROGRAM

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore