Saved Discoveries view
DCE device discovery
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When you create a device discovery process, information about that process is listed in this view. Information about the device group selected during the SNMPv1 and NetBotz Appliance discovery process is not included.
Wait a few minutes after a discovery process reports it is idle before you consider that it failed to discover all the devices it should have. The Data Center Expert server can take more time to list discovered devices in the Unassigned group in the Device Groups view, than it takes the discovery process to discover those devices.
Discovery entries
Use the Export Discovery Entries option to export information about the selected saved device discovery processes to a local file. Information about the device group selected during the SNMPv1 and NetBotz Appliance discovery process is not included.
Use the Import Discovery Entries display to import saved device discoveries from a local file.
Discovery entries file format
Use this file format to import SNMPv1 and NetBotz Appliance device discovery entries to the Saved Discoveries view from a local *.txt file. Information about the device group selected during the discovery process is not included.
Note: You cannot import device discovery entries for SNMPv3 or Modbus devices.
Format for SNMPv1:
SNMPv1:<IP Address or Range>:<port>:<timeout>:<retries>:<trap registration (true or false)>:<read community>:<write community>