webClient crashes when a pinpoint graphic is opened

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • webClient crashes when a pinpoint graphic is opened
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Sampath_Konda
    Sampath_Konda
  • Product_Support
    Product_Support
  • Chris_Asbury
    Chris_Asbury
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2854 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

webClient crashes when a pinpoint graphic is opened

Picard Product_Support
‎2018-09-07 10:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 12:19 AM

Issue

Opening Pinpoint in webClient results in one or all of the following error messages:

1.jpg

Unknown error.
Server:http://localhost/DNWACServerFactory/WACServerFactory.soap

2.jpg

C:\User\SEEB\AppData\Local\Temp\PPxtF\WPPCachw\PinFiles\???.pin contains an invalid path.

3.jpg

Runtime Error!

C:\Program Files\WebClientPinpoint\WPinpoint.exe

This application has requested the Runtime to terminate it in an unusual way.
Please contact the application's support team for more information.

Product Line

Andover Continuum

Environment

  • Windows Vista, Windows 7 and Windows Server 2008
  • Continuum Cyberstation 1.93

Cause

This is due to an error in the webclient install guide, page 88, where you are asked to edit the web.config file

Resolution

  1. Find the web.config file, normally in program files/continuum DNWACServerFactory, the file is called "web"
  2. Edit the file with notepad and delete the content
  3. Copy the following text in its place and edit the "machine name" to your PC name, in this example the name is "WORKSTATION1"

    <configuration>
             <system.runtime.remoting>
                     <application>
                             <service>
                                    <wellknown mode="Singleton" type="DNWACServerProxy.WACServerFactory, DNWACServerProxy" objectUri="WACServerFactory.soap"/>
                           </service>
                           <channels>
                                   <channel ref="http" machineName="WORKSTATION1">
                                   </channel>
                           </channels>
                    </application>
            </system.runtime.remoting>
            <system.webServer>
                    <security>
                            <requestFiltering allowDoubleEscaping="True"/>
                    </security>
                    <directoryBrowse enabled="true"/>
            </system.webServer>
    </configuration>

  4. Save changes to file and restart the PC. webclient and pinpoint should work normally now

NOTE:

If the "RunTime Error!" occurs on a Client machine and the operating system is Windows 10, download "MSXML 4.0 SP2 Parser and SDK' x86 file from Microsoft. This will resolve the access to the graphics from the client machine.

Here is the link:

https://www.microsoft.com/en-us/download/details.aspx?id=19662

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 5044
  • SampathKonda19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore