Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

"Invalid license key (inconsistent authentication code)" taclic vendor daemon error

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Invalid license key (inconsistent authentication code)" taclic vendor daemon error
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2500 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Invalid license key (inconsistent authentication code)" taclic vendor daemon error

Picard Product_Support
‎2018-09-11 07:49 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 08:51 PM

Issue

In TAC Vista 5.1.9 when trying to lock a license file to an end user dongle, the taclic vendor daemon starts briefly, but then stops again and you see the error "Invalid license key (inconsistent authentication code)" in the taclic.log file. Usually you only see that message if the license file has been tampered with.

8:48:28 (taclic) Invalid license key (inconsistent authentication code)
8:48:28 (taclic)       ==>INCREMENT Menta.View taclic 5.1 permanent 1 ISSUER=TAC \
ISSUED=30-may-2014 BORROW NOTICE=3424672 \
SN=FID__47eba299_146164ca427__7ec5 SIGN="13DC 795D AF25 E8ED \
D6EG 7BAA 8495 2ED7 B4B0 F6E4 EDD8 C3C1 6EAE 2BF0 598D 0759 \
AE4A 3C9E 391C A6ED B313 9971 369A 349C 8671 E194 2E42 E2DC \
8A9A 7905"

Product Line

TAC Vista

Environment

  • TAC Vista 5.1.9
  • License Server

Cause

An issue has been detected in TAC Vista 5.1.9 when locking a license file to an end user dongle. You see the error "Invalid license key (inconsistent authentication code)" in the taclic.log file. The error is located in the taclic.exe file.

Resolution

Contact PSS for a permanent hotfix for this issue, or download it from Exchange Download Center. 

Work around 1: Lock the license to the MAC address of the PC

  • Follow Rehosting a Vista 5 License on the FlexNet License Server to rehost a license file to a MAC address. 

Work around 2: Use a previous version of the taclic.exe file

  1. Access a PC having a previous version of the license server installed
  2. Locate the file "taclic.exe" and copy it - it's normally located in the TAC Vista installation folder under "License Server"
  3. Stop the license server on the PC having TAC Vista 5.1.9 installed
  4. Rename the original taclic.exe file to taclic_11.12.exe
  5. Paste the "taclic.exe" file you copied into the folder
  6. Start the license again 

In general when working with the license system on TAC Vista versions from 5.1.8 and above, this utility can come in handy: TACLicenseServer Settings.

Labels (1)
Labels:
  • TAC Vista
Attachments
TACLicenseServer Settings.zip
Tags (1)
  • Find more articles tagged with:
  • 16218
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of