Issue
Need to use a Xenta I/O module on another channel from the base device
Product Line
TAC Vista
Environment
- Xenta I/O Modules
- Xenta Programmable Controllers
- LON Channels
Cause
Using traditional I/O modules you are not allowed to span channels when placing your base unit and I/O modules.
Resolution
Use the 421A/422A or 451A/452A models. You can span channels by using SNVT based communication rather then Xenta group communication. You will be required to bind the values to the base unit.
See Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node for more information on configuring the Xenta I/O modules for stand alone operation.