Xenta I/O modules cannot be on a different channel from the base unit
  • Xenta I/O modules cannot be on a different channel from the base unit
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • SESA116857
    SESA116857
‎2018-09-07 12:57 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:49 AM
Need to use a Xenta I/O module on another channel from the base device
TAC Vista
  • Xenta I/O Modules
  • Xenta Programmable Controllers
  • LON Channels
Using traditional I/O modules you are not allowed to span channels when placing your base unit and I/O modules.
Use the 421A/422A or 451A/452A models. You can span channels by using SNVT based communication rather then Xenta group communication. You will be required to bind the values to the base unit.
See Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node for more information on configuring the Xenta I/O modules for stand alone operation.