Workplace Tech 5.9.x and EcoStruxure Building Operation Workplace Tech Editor use with Visio 2013 and 2016

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Workplace Tech 5.9.x and EcoStruxure Building Operation Workplace Tech Editor use with Visio 2013 and 2016
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RandyDavis
    RandyDavis
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4067 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Workplace Tech 5.9.x and EcoStruxure Building Operation Workplace Tech Editor use with Visio 2013 and 2016

Picard Product_Support
‎2018-09-10 07:55 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-06-23 06:12 AM

Issue

Proper handling and preparation of existing .vsd files help eliminate the crashing and lockup of the Visio application.

Product Line

EcoStruxure Building Operation, TAC IA Series

Environment

  • Workplace Tech Editor EcoStruxure 1.9.x - 3.2.3
  • Workplace Tech 5.9.1 - 5.9.4
  • Visio 2013, Visio 2016
  • Note: This does not apply to Workplace Tech Editor EBO 2022 (and newer) and Workplace Tech 5.10.x

Cause

The product is affected by the version of Visio in use as well as the file size and unused objects in the drawing.

Resolution

  1. When using Workplace Tech 5.9.x with Visio 2013 or 2016, the file has to be opened in "Compatibility Mode." DO NOT CONVERT.
    Illustration 1
    Visio2013_1.jpg
  2. While the .vsd file is open in Visio, not in Workplace Tech, use the "Reduce File Size" option and select the boxes in Illustrations 1&2.
    Illustration 2
    Visio2016_1.png
  3. In Visio 2016, after opening the "Inspect Diagram," (Illustration 3), select the first 3 boxes in the "Reduce File Size" option (Illustration 4).
    Illustration 3
    Visio2016_2.png
    Illustration 4
    Visio2016_3.png
  4. Save the file for use in the Workplace Tech Project or to be imported into your AS-P as a .vsd. Add the "cleaned" file to your project or import it to Workplace Tech Editor. Make sure the Visio 2013 or 2016 is at the most recent version and build. You can find this under the file/account/About Visio. If Version 1802 is available in your Microsoft Office update Channel, use it. Version 1801 was used in testing. For Visio 2013 Build 15.0.4971.1000 MSO 15.0.5007.1000 was tested (Illustration 5)
    Illustration 5
    Visio_2.png
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (9)
  • Find more articles tagged with:
  • 1.9.2.45
  • 19740
  • 5.9.3
  • launched
  • longer
  • RandyDavis22
  • starts
  • upgraded
  • wptech
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore