Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Working principle of the Bond Sensor Input

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Working principle of the Bond Sensor Input
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Ramaaly
    Ramaaly
  • AdamSteele
    AdamSteele
  • Dave_Shore
    Dave_Shore
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5323 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Working principle of the Bond Sensor Input

Product_Support
‎2018-09-06 12:20 PM

Last Updated: Ramaaly Contributor ‎2025-09-03 12:36 PM

Issue

    • Will the Bond Sensor Input Channel contribute to the Door Forced and Door Ajar alarms? If so, does it have to be in conjunction with the Door Switch Input Channel?

Product Line

Andover Continuum

Environment

  • Continuum Access Control Products
  • CX9900
  • CX9680
  • Continuum AC-1 IO Module
  •  AC1A, AC1Plus
  • ACX5720, ACX5740
  • CX9702
  • ACX781

Cause

Not sure how the Bond Sensor works in relation to the Door Switch and the various Door Alarm states.

Resolution

BondFailure is an attribute of the Door object that represents a fault with the Bond Sensor.

The way this works is if Valid Access = True and the Door Switch = Open and the Bond Sensor = Open, then BondFailure = False.

If Valid Access = False or the system sees the Door Switch = Closed but the Bond Sensor = Open then you will get a BondFailure = True.

This is another attribute (BondFailure) that can be monitored with an AlarmEnrollment in addition to the DoorForced and DoorAjar attributes. A Door Switch needs to be used for the Bond Sensor to operate correctly, otherwise BondFailure will always be False after a ValidAccess if there is no Door Switch value.

Note: The actual value of the BondSensor attribute in the Door object may not seem to update properly if monitoring with a ListView. For this to show the correct BondSensor value make sure that the attribute Source is set to "Live" instead of the default "Database".

Note2: A bond senor (usually an output from a maglock) should not be used as an alternative to a door switch, as it does not give indication of the door position.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 7970
  • RamaAly25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.