Wireshark capture ring buffer for continuous capturing

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Wireshark capture ring buffer for continuous capturing
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • David_Purser
    David_Purser
  • AbeMeran
    AbeMeran
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
11385 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Wireshark capture ring buffer for continuous capturing

Picard Product_Support
‎2018-09-10 10:21 AM

Last Updated: Picard David_Purser Picard ‎2022-08-22 11:52 AM

Issue

In order to troubleshoot random network issues, it is sometimes necessary to set up Wireshark to capture network traffic for an extended period of time. As Wireshark runs it decodes packets and its data structures grow. This causes performance issues and eventually, Wireshark may simply run out of virtual memory and stop capturing or crash.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

Wireshark

Cause

Need to capture network traffic using Wireshark for an extended period of time.

Resolution

Open Wireshark and follow these instructions:

  1. From toolbar, select Capture -> Options
  2. On the Input tab, select input adapter. If necessary set capture filter.
  3. On the Output tab, perform the following:
    1. Browse capture file location and provide a filename. A timestamp will be added to the filename as a suffix.
    2. Ensure output format = pcapng
    3. Check Create a new file automatically
    4. Check After 1 and change seconds to hours
    5. Check when time is multiple of 1 and change seconds to hour
    6. Check use a ring buffer with X files. (Recommended settings are 96 hours (4 days) or 168 hours (1 week) so can retrieve files after long weekend or 1 week, respectively). WiresharkCaptureOutput.png
  4. On the Options tab, perform the following
    1. Check last selection and change to 744 hours. (Recommended to capture for 31 days without stopping). WiresharkCaptureOptions.png
  5. When an event happens, gather a capture with the timestamp before and after the event. One can ZIP the .pcapng files to save space when transferring.

 

NOTE: More recent versions of Wireshark ( 2.4.1.21317 ) make it very easy to set up a ring buffer from the Output tab of the Capture options.

RingBuffer.PNG

For older versions of Wireshark 1.x use the steps below

When capturing data, Wireshark actually uses a capture utility called DumpCap to do the actual data capture. DumpCap does not decode packets as they come in and thus has a smaller memory footprint which remains constant. The only remaining concern is the size of the capture file or files which can be specified when starting the ring buffer to keep them from growing too big.

DumpCap is found at the location where the Wireshark program resides which can be seen if you go to Help\About Whireshark\Folders

  1. Determine the index to the Ethernet adapter you need to capture on. In this example, the traffic seen by the Broadcom NetXtreme Gigabit Ethernet adapter will be captured. Index 1 is specified when starting DumpCap.
  2. Execute DumpCap with the following options
    dumpcap -i 1 -b files:3 -b filesize:10 -w C:]temp\abe.pcapng
    • -i 1 specifies tp capture on the network adapter with an index of 1
    • -b file: 3 specifies to use a 4 file ring buffer.
    • -b filesize:10 specifies to limit the file size to 10 KB (*** for a real life capture this number would be much bigger like say 100/200 MB)
    • -w c:\temp\abe.pcapng specifies location and prefix for the three files
  3. In the screenshot below we can see the files in the ring buffer being used, once a file reaches the specified limit, the capture continues at the next file, files are names using the specified prefix as well as a date-time stamp that is updated each time utility dumps captured data in the file.
    Care should be taken to stop the capture as soon as possible once the issue under investigation takes place and before the ring buffer wraps around and overwrites the data.
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 19474
  • AbeMeran20
  • DavidPurser22
  • PeterLarsen24
  • ringbuffer
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore