White space or blank screen when first launching webclient from a browser

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • White space or blank screen when first launching webclient from a browser
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4951 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

White space or blank screen when first launching webclient from a browser

Picard Product_Support
‎2018-09-10 05:39 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:35 PM

Issue

Using the correct URL to launch webclient and there is only white space

Product Line

Andover Continuum

Environment

  • Webclient
  • Windows XP
  • Windows Vista
  • Windows 7
  • Windows Server 2003
  • Windows Server 2008

Cause

ActiveX controls were not installed from the Server onto the browser PC.

Certain versions of browser (IE8) disable unsigned activex controls which we use for webclient

Resolution

It is possible that if this is happening on a domain that there is a group policy in place restricting access. Try the browser on the webClient PC or a laptop directly connected to the webClient PC.

  1. Check the compatibility matrix to see if the version of your browsers are supported with that version of webClient.
  2. Ensure the Activex controls were installed
  3. Turn Off Pop-up blocker.  Internet Explorer> Tools>Turn Off Pop-up blocker
  4. Internet Explorer> Tools> Internet Options> Security> Select the correct Zone (i.e. Internet, Local, trusted).
  5. Click Custom Level button
    1. Select Enable for Automatic prompting for ActiveX controls
    2. Select Enable or Prompt for Download signed ActiveX controls
    3. Select Enable or Prompt for Download unsigned ActiveX controls
    4. Click OK, OK
    5. Close Internet Explorer and try again.
  6. If it is still not working, clear the cache (http://support.microsoft.com/kb/260897) and try again.
  7. If the PC is 64 bit and the webclient version is not 1.94 and above, that could also cause this.
  8. In extreme cases removing and reinstalling .net, IIS and webclient may be necessary.
  9. Verify that the version of SQL Server is compliant with the version of Continuum that is being used. Ex. SQL Server 2000 with SP3 (instead of SP4) isn't compatible with webclient 1.93
  10. Check Removal of MS KB2858725 Dot Net 4.5.1 causes issues with Web Servers IIS Functions related to .Net 4.5
  11. Reinstall webclient
  12. Lastly, a reformat of the hard drive an complete reinstall.

Note: If the white space happens in just the personnel area and this is 1.74 remove .net version greater than version 2

In IE 9 and IE10 use compatibility mode

IE11 is not currently not supported in a 1.94 SP1

** Webclient 2.0 new alarmview is blocked by IE setting "Block pop-ups" **

If you receive "Internet Explorer blocked a popup from webClient IIS" after logging into webclient then turn of the pop-up blocker for this or all sites. Open Internet Explorer > Tools > Pop-up Blocker > Turn off Pop-up Blocker

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 7021
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore