Remote Alarm Manager Unable to Send Long Text Messages in Sigma 4.05
  • Remote Alarm Manager Unable to Send Long Text Messages in Sigma 4.05
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-06 02:26 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-21 05:53 PM
When using Remote Alarm Manager (RAM) with Sigma 4.05, Long Text messages cannot be sent as part of the RAM message.
Satchwell BAS & Sigma
  • Sigma 4.05
In Sigma versions prior to 4.05, Long Text messages were stored individually in the Sigma\Data\LongText folder.
Sigma 4.05 introduced a new unified format:
  • File: LongText.rec
The Remote Alarm Manager does not recognize this new format, resulting in failure to send Long Text messages.
Scenario 1: Upgrading an existing Sigma site to 4.05 with RAM installed
If RAM needs to use Long Text messages:
  1. Upgrade the Sigma system to version 4.05.
  2. Retain the original Sigma\Data\LongText folder.
  3. Create messages manually using the steps below.
Scenario 2: Adding a new Long Text message
  1. Use the Sigma 4.05 Long Text editor to create the message.
  2. Copy the message.
  3. Save it as Ltxt???.txt in Sigma\Data\LongText, where ??? is a unique identifier.
Scenario 3: Configuring a new Sigma 4.05 system with RAM
  1. Create a folder: Sigma\Data\LongText.
  2. Use the Sigma 4.05 Long Text editor to create the message.
  3. Save it as Ltxt???.txt in the folder, using a unique number for ???.
Additional Notes
  • Ensure that the Sigma\Data\LongText folder exists and is correctly populated with .txt files for RAM to function properly.
  • This workaround allows RAM to access Long Text messages despite the format change in Sigma 4.05.
  • Satchwell BAS & Sigma
Tags (2)
  • 3982
  • CraigEllis25