When attempting to apply a lonmaker connection you get this error (Subsystem: NS Connections, #14)
  • When attempting to apply a lonmaker connection you get this error (Subsystem: NS Connections, #14)
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
‎2018-09-06 03:16 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-15 09:11 PM
This is the error message that is displayed when you attempt a connection.
You get a LonMaker Error message when applying a connection. "this connection would violate a network variable selector constraint, which limits the number and type of NVs a device that may use the same selector. The automatic use of NV aliases was unable to avoid this) there may be no aliases available).
TAC Vista
LonMaker
One NVO is attempting to be connected to multiple NVI's in one device.
LonMaker does not allow the same NVO to be connected to the same receiving device more than once.
Add extra NVO's in the sending device to allow for a one-to-one binding with the receiving NVI's.
Tags (4)
  • 8155
  • mutlicast
  • peer
  • unicast