Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

When a TGML graphic is set to "Display on alarm" it is not opened when that alarm is triggered

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • When a TGML graphic is set to "Display on alarm" it is not opened when that alarm is triggered
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1580 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

When a TGML graphic is set to "Display on alarm" it is not opened when that alarm is triggered

Picard Product_Support
‎2018-09-07 08:56 AM

Issue

A TGML graphic has been selected in the Attachments options of a Alarm and also been selected to "Display on Alarm" but does not auto display

Environment

StruxureWare Building Operation 1.3 and above

Cause

There are two reasons that can stop this functionality working.

  1. The alarm has already been triggered and not cleared from the alarm Queue.
  2. There is no Alarm View displayed in the users configuration. If you cannot see the alarm in the users workspace the Graphic page will not be displayed.
  3. In StruxureWare Building Operation 1.3 if using custom Alarm Views (i.e. not defined in the default workspaces) the Attached "Display on Alarm" does not function.  This is corrected in release 1.4.0.818 and above. 

Resolution

Check that the user has an alarm view visible within their login. An example of this is the default Workspace Administrator. In its default setting the Alarm Pane is not set to display.

If you log in using the Engineering Workspace the Alarm Pane is displayed and the function works.

Here is the two default workspaces that show the alarm pane option

1. Administration Workspace with the Alarm pane not set

2. Engineering Workspace with the Alarm pane set to be displayed

 

The alarm will also need to be returned to normal and acknowledged so it is not left in the alarm queue.

The display on alarm function works on the alarm entering the alarm queue, if it is already present in the queue the display on alarm option will not work.

StruxureWare Building Operation Release 1.4 Note:

In StruxureWare Building Operation 1.3 if using custom Alarm Views (i.e. not defined in the default workspaces) the Attached "Display on Alarm" does not function.  This is corrected in release 1.4.0.818 and above. 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 14433
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of