Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What are the differences between Standard Continuum Import/Export and Continuum BACnet COV?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are the differences between Standard Continuum Import/Export and Continuum BACnet COV?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2188 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are the differences between Standard Continuum Import/Export and Continuum BACnet COV?

Picard Product_Support
‎2018-09-06 02:59 PM

Issue

What are the differences between Standard Continuum Import/Export and Continuum BACnet COV? What issues can arise from programming a Bacnet system if you are using the Continuum Import/Export concepts.

Product Line

Andover Continuum

Environment

  • Standard Continuum Import/Export
  • Continuum BACnet COV

Cause

Information on Continuum import/export and BACnet COV concept to help select the method that meet the environment.

Resolution

Using standard Continuum import/export where one or more controllers reference a point from another controller creates a relationship in the controllers such that whenever the exported value changes (or exceeds the threshold setting), the point value will be sent out in a broadcast to the network and the controllers that are looking at that point will intercept this single broadcast message and use the new value in their programs. It is very efficient in that no matter how many controllers on the network require a point value from a single controller, only one export message is required. The down side of that is that if there was a network interruption when the message was sent, one or more of the receiving controllers may miss the data update. For critical data exchange, especially if the value rarely changes, such as a schedule point, the use of a refresh program should be used to occasionally retransmit the value by setting the refresh attribute of the point to true.

BACnet utilizes Change of Value (COV) data sharing. The main difference here is that for every controller that references a point from another controller, an individual subscription for that point is registered in the exporting controller. So if 10 controllers wanted the same point exported from one controller there would be 10 subscriptions made to that controller. When the point value exceeds the COV Increment (which is equivalent to threshold) there are 10 individual point to point messages sent to the 10 subscribing controllers. The benefit here is that the delivery of the data to all the subscribers is guaranteed. The down side is that there is much more traffic on the network and much more strain put on the exporting controller. Although the data exchange is very reliable, if you were, for instance, to have an MSTP controller possess a global OAT sensor, and 100 other controllers wanted that value exported, every change in value would require 100 point to point messages to send it to the 100 subscribers. MSTP devices default to a Max_Info_Frames of 2, which means that the controller can only deliver 2 of these messages when it gets a chance to talk on the network. The MSTP controller only gets a chance to talk after every other controller on the network has had a chance to, plus the BCX controller which is interlaced between each MSTP controller when using enhanced MSTP. So, if there were 100 MSTP controllers on the network, the exporting controller could only send updates to two of his 100 recipients every 200 token passes on the MSTP network. The data would get backed up, especially if the value was frequently changing, so the updates may never get out.

If this amount of data sharing is required in BACnet, the best method to perform it would be to first set the COV Increment to a reasonable number to limit the amount of exports required, and then map the point in one or more BCX level controllers which have much more bandwidth on the network and capability of data sharing and let them export the COV's to the required recipients.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2554
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore