What are Handles and what causes duplicates / mismatches

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are Handles and what causes duplicates / mismatches
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1708 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are Handles and what causes duplicates / mismatches

Picard Product_Support
‎2018-09-10 01:18 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:37 AM

Issue

How can duplicate Handle errors be fixed?

Product Line

Andover Continuum

Environment

  • All versions of Continuum
  • CX, i2 and infinet Controllers

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

An SQL database gives every object a unique handle that is used internally to reference that object. If Continuum requests a value from an Input point that has handle 1234, but that controller has handle 1234 for example as a TimeDate point, then problems will ensue.

Every object in the DB has a unique handle. This includes all classes: points, programs, graphics, reports, schedules, etc.

Duplicate handles can be caused on sites where engineers use multiple databases during commissioning on new panels (maybe a Single User on their laptop), It can also be caused by importing dump files with handles created from other databases, or just from database corruption on the server from failures etc. It can also be caused by the use of an Infinity LSX280 see Handle mismatch issues.

Resolution

  1. Usually reloading the controller will re-sync the controller and all of its object handles back to the site database.
  2. If the DB has become corrupted, run the analyzer and try to fixup (Clean) any issues
  3. You may even have to manually delete the offending objects, running the Import Export Fixup utility (See How to run the Import/Export Fixup Utility)
  4. Follow this with a controller reload
  5. Worst case would be to revert to a backup DB if it is found to be corrupt.

To avoid issues altogether, it is best to engineer a project all from a single DB and take care when importing dump files.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 11394
  • DavidShore20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.