WebReports - Changing the PC name.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WebReports - Changing the PC name.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3148 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WebReports - Changing the PC name.

Picard Product_Support
‎2018-09-07 02:22 PM

Last Updated: Picard RobertAndriolo Picard ‎2023-05-01 05:47 PM

Issue

There is a requirement to change the WebReport server name.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Report Server
  • Building Operation WebReports
  • SQL Server

Cause

Changing the WebReports server name after the WebReports software has been installed, does not change the PC name references in the WebReports or the database.

Resolution

If possible, ensure that the PC name will not need to be changed after the PC has been configured for WebReports.

If having configured a PC for WebReports, the PC name has to be changed, then backup all SQL data first then uninstall the WebReports software, ensuring that the following process is followed step by step.

Below is an overview of the uninstall process, the exact details are shown in section 15.11 of the WebReports Reference Guide.

15.11 Uninstalling WebReports

Complete the following tasks to uninstall WebReports and the WebReports database:

  1. Uninstall the WebReports application and services using Windows Control Panel
  2. Delete the WebReports database using Microsoft SQL Server Management Studio
  3. Delete the WebReports reports using SQL Server Reporting Services Report Manager
  4. Remove the virtual directories for WebReports and the WebReports service using Internet Information Services (IIS) Manager
  5. Remove the WebReports application pools using the Internet Information Services (IIS) Manager
  6. Delete the appuser and IUSR accounts (if they exist) using SQL Server Reporting Services Report Manager, Microsoft SQL Server Management Studio, and Windows Computer Manager.

Please note that having uninstalled the WebReports software, follow the steps shown on the following Microsoft website: Rename a computer that hosts a stand-alone instance of SQL Server - SQL Server

If this procedure fails then SQL Server should also be reinstalled after having changed the PC name first.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4981
  • RobertAndriolo23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.