Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Web Pinpoint displays different animation file(s) while Cyberstation's pinpoint displays correct animation files.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Web Pinpoint displays different animation file(s) while Cyberstation's pinpoint displays correct animation files.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SangKim
    SangKim
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1330 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Web Pinpoint displays different animation file(s) while Cyberstation's pinpoint displays correct animation files.

Picard Product_Support
‎2018-09-06 02:28 PM

Issue

Web Pinpoint displays different animation file(s) while Cyberstation's pinpoint displays correct animation files.

Environment

Cyberstation graphics

Cause

This issue happens when you create pinpoint graphics with different animation controls using the same animation file names. Although the files that are named the same are from different folders, Web pinpoint will not distinguish one file from the other.

Resolution

In order to provide faster response to Remote PC's WebPinpoint graphic, Continuum WebClient server caches animation bitmap files in a subfolder (..\Temp\Animation) under the graphic folder.

As the file name is the unique key in the cache folder, it is required to use unique names for each animation bitmap file if the files contain a different animation control on a graphic.

For example, first graphic displays a Fan animation with 4 bitmap files named as FAN1, FAN2, FAN3, FAN4 from below folder;
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup1\FAN1.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup1\FAN2.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup1\FAN3.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup1\FAN4.bmp

And the second graphic displays a Fan animation with 4 bitmap files named as FAN1, FAN2, FAN3, FAN4 from below folder;
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN1.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN2.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN3.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN4.bmp

It is required to change the file names for the second graphic to be unique as below;
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN5.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN6.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN7.bmp
C:\...\NewGraphicsFiles\ImageLibrary\Animation\FanGroup2\FAN8.bmp

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3885
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of