Continue
  • My Subscriptions
  • Events
Viewed from the ES, an AS drops offline every 5-10 minutes
  • Viewed from the ES, an AS drops offline every 5-10 minutes
  • Dave_Shore
    Dave_Shore
  • Alan_Wood
    Alan_Wood
  • BillNeville
    BillNeville
‎2018-09-06 10:45 AM
Last Updated: DavidFisher Champion ‎2019-08-14 06:52 AM
Automation Server is going online and offline when viewed from an Enterprise Server.
NOTE: Depending on the network setup/IP switch arrangement, having a duplicate Automation Server (AS) IP address can manifest itself by the AS continually resetting itself (Status LED going red, then flashing green, then solid green, followed by red again) over a 1 to 2 minute cycle.
  • SmartStruxure Enterprise Server
  • StruxureWare Building Operation Workstation
  • Automation Server
Duplicate IP address assigned to the AS. IP conflicts will cause the AS to go offline in the ES.
  1. Check that the AS has a unique IP address on the network.
  2. If not, consult the IT department to verify that they can provide a unique static IP address.
  3. Also, isolate the AS temporarily using a switch and see if the issue stops.
Tags (2)
  • 12180
  • blinking