Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Viconics stats and controller offline alarms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Viconics stats and controller offline alarms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • CraigEl
    CraigEl
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1503 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Viconics stats and controller offline alarms

Picard Product_Support
‎2018-09-10 11:10 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:14 AM

Issue

Viconics stats are only showing as offline in Continuum using the "controller status" notification when being accessed

Product Line

Andover Continuum

Environment

  • Continuum
  • Viconics Stats

Cause

Viconics BACnet stats must be probed in order to return alarms

Resolution

There are 3 probe types that can be set up in Continuum. Probe, ProbeOnDemand and ProbeOff. 

These types can be  configured in Cyberstation and in the Viconics Stat from Continuum Explorer  (Edit>General Tab>ProbeType drop down selection) 

"Probe Time" can also be adjusted on the Cyberstation (default is 60 seconds)

Testing Results

  1. Cyberstation Probe Type changed to "Probe", Probe Time=60 seconds. Viconics stat set to it's default of "Probe Off"
    Remove mstp connector result: no alarm until the Viconics stat is opened (This probes the device)
  2. Cyberstation Probe Type changed to "Probe", Probe Time=60 seconds. Viconic stat set to "Probe"
    Remove mstp connector result: alarm comes in automatically after 60 seconds

Probe Type and Probe Time Definitions (Continuum Help) 

Consider and these options and their affects on the system when making a selection

  • Probe - Probing occurs at the interval specified in Probe Time.  The default is 60 seconds.  The advantage of this is that CyberStation detects a device going offline regardless of whether or not CyberStation is attempting communications with the device. The disadvantage is excess probe traffic for devices.
  • ProbeOnDemand - Probing does not occur unless a communications transaction with the target device fails. Once a transaction fails then probing occurs at the interval specified in Probe Time until the device comes back online. The advantage is that additional requests to the controller fail immediately. The disadvantage if that node failure is not detected  until a CyberStation application needs to communicate with a controller. 
  • ProbeOff - Probing does not occur. The advantage is that there is never probe traffic to the device. The disadvantage is that each request to the device fails only after the transaction times out.

Also see the following article related to Viconics stats and performance: Problems and cautions when communicating with TAC (Viconics) Bacnet communicating thermostats

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 11957
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore