Veris temperature transmitter - control system is reading an inaccurate temperature reading
  • Veris temperature transmitter - control system is reading an inaccurate temperature reading
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
‎2018-09-11 02:33 PM
Veris temperature sensor with voltage transmitter output
The Veris sensor and the controller are located at different locations and using a different common as they are being powered by different power sources.
Refer to the sensor's installation instructions and ensure that the sensor and controller uses the same common.