Values are indicating [??787] in Workstation.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Values are indicating [??787] in Workstation.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1671 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Values are indicating [??787] in Workstation.

Picard Product_Support
‎2018-09-06 02:23 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-12-05 03:32 PM

Issue

Point values are not displayed in Vista Workstation.  Instead, all of them say [??787].

Product Line

TAC Vista

Environment

Vista Workstation

Cause

The most common cause of the ??787 error message is a mismatch in the XIF between the device and the Vista database.  It may also be duplicate SNVT names in the XIF.

Resolution

There are a few common troubleshooting techniques that have been applied successfully to the ??787 error and resolved the issue.  The first is to upload parameters from the device.  The second is to browse the correct XIF to the device to eliminate any mismatch.

Upload parameters

  1. Right-click on the device in Vista Workstation.
  2. Select Upload Parameters.
  3. Shut down Vista and restart.

Make certain you are using the correct XIF

  1. The only way to be absolutely certain that the XIF in the device matches the one in the database is to upload the XIF from the device.  You may need to create a dummy LNS database to do so.  Add a generic device and commission with the option to upload the XIF from the device.
  2. Update the Vista database.  Again, this may need to be a dummy Vista database.
  3. To obtain that XIF, right-click on the device in Workstation and select Properties.  The XIF File tab lists the database copy of the XIF file (hexadecimal file name) that can be found in the Vista database directory in the $thisfil folder.

Browse the correct XIF into the Vista Workstation

  1. If you are certain you have the correct XIF, right-click on the device in Vista Workstation.  Select the XIF File tab.
  2. At the bottom under Source File, click the "..." button and browse to the XIF file.
  3. Click okay.  Log out of Workstation and log back in to see the changes take effect.
  4. It may then be necessary to right-click on the controller and select Commission and Download.

Remove duplicate SNVTs

  1. Open the XIF in a word editor (Notepad, Wordpad)
  2. Find the duplicate SNVT name using the Find feature
  3. Rename one of the SNVTs to a unique name.
  4. Use the above steps to browse this new XIF into Vista Workstation.

XIF file contains internal variables

  1. Open the XIF in a word editor (Notepad, Wordpad)
  2. Search for the variable whose value displayed as [??787]
  3. If the variable is not listed in the XIF file, it is possible that this is an internal variable which Vista cannot read a value from
  4. Contact the manufacture of this device and ask if they can expose the value with a network variable in order for Vista to read it.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4098
  • PeterLarsen21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore