Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Using the PFC object in an MPM-VA

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using the PFC object in an MPM-VA
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MaximeLaudren
    MaximeLaudren
  • SaidSawan
    SaidSawan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1766 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using the PFC object in an MPM-VA

Picard Product_Support
‎2018-09-06 08:40 AM

Last Updated: Lieutenant MaximeLaudren Lieutenant ‎2022-08-18 09:35 AM

Issue

Unsure how to use the settings in the VAV Flow object

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager (MPM)

MPM-VA

Cause

Cannot change the units of the output

Resolution

For Variable Air Volume (VAV) Flow configuration, it is recommended to use the Kf method when setting up an MPM-VA

In the PFC calculation, the Kf factor represents the flow (Q) for a measured dP on the flow ring of 1 Pascal (Pa). The flow sensor on the MPM controller (AI21) measures dP in inches of water column (in w.c.). With a conversion of 1 in w.c. = 250 Pa, we obtain this formula:

Kf = Q [cfm] / (sqrt(250 x dP[in w.c.])) or,

Q [cfm] = Kf * (sqrt(250 x dP[in w.c.]))

 

Calibration/Balancing:

A typical VAV box should have a theoretical Kf factor provided by the manufacturer. This Kf value must be used in the in the PFC object when balancing VAV systems. Next, using instruments such as an air flow capture hood, technicians must compare the output flow from the PFC object and the actual measures air volume. If the values do not match, the measured value along with the value of AI21 must be entered in the above equation to produce a new Kf factor. The new Kf value will then be used in the PFC object to finalize the calibration

For example if the measured air volume is 200 cfm and AI21 is 1.2 w.c., the new Kf will be:

Kf = 200 / (sqrt(250 x 1.2)) =11.55

Important notes:

-Even though the Kf units show "Liters per second", the "Flow output value" will be in "Cubic feet per minute" (CFM) if the value of Kf is based on CFM values. If the Kf is based on LPS, the output will be in LPS

-Every time the Kf factor is changed in the PFC object in the MPM, it will take up to 2 minutes before the output flow changes to the new value

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (3)
  • Find more articles tagged with:
  • 18473
  • MaximeLaudren22
  • pressure
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of