Issue
Will an i2 device work on an existing installation that uses a CMX241 controller?
Environment
Continuum
CMX241
Infinet
Cause
An installation that has a CMX controller with infinet and the infinet 1 controller needs to be replaced with an i2.
Resolution
The CMX241 controller will recognize an i2 controller, but it will handle it as if it is an infinet1 controller.
Some infinity system variables and their functionality will not be recognized such as accrestart mode, accstatusflash, etc...
The replacement for the CMX241 is the BCX9640