Using STR-350 override with a Xenta 121
  • Using STR-350 override with a Xenta 121
  • Jonas_Brissman
    Jonas_Brissman
‎2018-09-07 03:36 AM
Last Updated: Administrator CraigEl Administrator ‎2025-04-04 05:06 PM
How do you integrate a time schedule in a Xenta programmable data manager, the occupancy command for a Xenta 121, and the override button on the associated STR-350 stat in an LNS system where everything is connected using SNVTs?
TAC Vista
Xenta 121
The desired outcome is to have all of the occupancies synchronized at all times. This will ensure the stat shows the current effective setpoint, the 121 runs the unit when appropriate, and the effective occupancy is available from the front end.
  1. Place the STR-350 in between the Xenta programmable occupancy output and the input command of the Xenta 121.
  2. Bind nvoOccupancy (user-defined name) output from Xenta programmable to nviEffectOccup of STR-350.
  3. Bind nvoOccManCmd output from STR-350 to nviOccManCmd of Xenta 121.
Tags (3)
  • 4250
  • JonasBrissman25
  • thermostat