Using I/NET trends in StruxureWare Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using I/NET trends in StruxureWare Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Derrick_Ratliff
    Derrick_Ratliff

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2399 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using I/NET trends in StruxureWare Building Operation

Picard Product_Support
‎2018-09-10 12:00 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:35 PM

Issue

Using I/NET trends in StruxureWare Building Operation

Product Line

EcoStruxure Building Operation, TAC INET

Environment

  • I/NET
  • StruxureWare Building Operation 1.3

Cause

Ideally trends should reside in the controller rather than at the sever level as this prevents sample data loss due to communication errors.

Resolution

Before you begin, ensure that all I/NET trends are set up correctly and trend data is visible. For assistance with this see Setting Up I/NET Seven Trends. Ensure that messaging is working so that SmartStruxure receives I/NET messages, and ensure that all controls have points to be trended, are already added to the I/NET Interface.

NOTE: For the Enterprise Server level integration, the I/NET Trend Object must be configured as a Seven Trend. For the Automation Server level integration, this is not required, therefore skip to step 3.

  1. In I/NET, Select Trends>Data Inquiry/Edit
  2. View the trend you wish to see in SmartStruxure and verify that it has data.
  3. Open StruxureWare Workstation
  4. Refresh the system tree and upload any I/NET controllers that do not show a green dot.
  5. Right click on the I/NET Interface and select New>Value
  6. When the "Create Object" Window appears, name the value and click "Create"
  7. The Value will appear in the I/NET Interface
  8. Right Click on the newly created Value and select "Properties"
  9. Locate the "Point to Trend" Field
  10. Click on the "..." and select the point object you wish to trend
  11. Click the select button
  12. Verify that the Point to Trend field is correct and Click OK
  13. Wait enough time for several samples to populate.
  14. Right click on the Value object in the I/NET interface and select View>Trend log lists>New Trend log list
  15. The New Trend log List should open and values should visible.
  16. The Trend Value object under the I/NET interface will now function the same as a trend object in StruxureWare.
  17. If you wish for the I/NET trend to show up as part of an Energy Report, you will need to Ensure that the Extended Trend Log is referenced in a Meter's "Meter Trend Log" property

NOTE:

For the Enterprise Server Level Integration, In order for the initial connection between the StruxureWare Value Object and the I/NET Seven Trend to be enabled, the following conditions need to be true:

  • The Controller with the I/NET point being trended must not require an upload
  • The Controller with the I/NET point being trended must have a current save file
  • The Controller with the I/NET point being trended must be online
  • The I/NET workstation located on the Enterprise Server must be masked to receive data from the trend log on the controller to the Seven Trends Definition

For the Automation Server Level Integration, In order for the initial connection between the StruxureWare Value Object and the I/NET Seven trend extension to be enabled, the following conditions need to be true:

  • The Controller with the I/NET point being trended must not require an upload
  • The Controller with the I/NET point being trended must be online
  • The I/NET trend object and point object must have some level of masking so that the data will leave the controller.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 8346
  • beta
  • release
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore