Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Setting Up I/NET Seven Trends

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting Up I/NET Seven Trends
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1811 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting Up I/NET Seven Trends

Picard Product_Support
‎2018-09-06 03:10 PM

Issue

Setting Up I/NET Seven Trends

Product Line

TAC INET

Environment

I/NET Seven

Cause

Problems configuring Trend Data

Resolution

I/NET displays this window when you select Add Trend, Add Cell, or Modify from the Seven Trends Definitions window. You must define the following information:

Trend Definition only

  1. Select the desired point from the Point Selection dialog. Only one point may be selected for a trend definition. This field cannot be edited once the trend definition is saved. This field is not available for cell definitions.

Note: You may click the ... button to return to the Point Selection dialog at any time during a new trend definition. However, once the trend definition is saved, you cannot change the selected point.

  1. Enter a unique Name for this trend or cell definition, up to 30 characters. The default name for trends is in the format Point Name -- --Trend Type if you are connected to the controller, and Point Address -- Trend Type if you are not connected. The default name for cells is in the format Cell Number -- Trend Type.

Note: If you do not enter a name, the default name will change automatically with the point (or cell number) and trend type selection when you are creating a new trend. You may change the name of a trend or cell definition at any time without loss of data.

  1. Choose a Type from the drop-down list. This field cannot be edited once the definition is saved.

    Discrete Sample — Store the discrete state of a point at regular sample intervals. The point can be a DI, DA, DM, DC, or DO point defined with a TR extension.

    Analog Sample — Store the analog value of a point at regular sample intervals. The point can be an AI, AO, GI, GO, or PI point defined with a TR extension.

    Runtime — Store the daily runtime minutes for a point or points. The points can be DI, DC, or DO points defined with an RT extension.

    Consumption — Store the daily-consumed value of an accumulator point or points. The points must be PI points defined with a CN extension.

    Demand — Store the KWH, Peak KW, and time of Peak KW values on a daily basis for a particular demand meter. The point must be a PI point defined with a DC extension.

    Override — Store individual KWH values, shared KWH values, and override runtime on a daily basis for a specific zone of a Model 7750 Building Manager. The point can be a DC or DO point defined with an OB extension.
     
  2. Define Transient Duration in days. The trend can be configured to automatically discard the oldest trend data after a time period you specify (1 to 45 days).

Note: If you wish to archive Seven Trends data, the transient duration must be set to zero (0), indicating that the data should not be discarded. Only samples with a transient duration of zero can be archived.

  1. Enter a Cell Number (1–1023). The cell number must be greater than zero (0) in order for Seven Trends to store sample information. This field is provided for backward-compatibility with older versions of I/NET, and can be used to group samples in reports.

    If you are creating a new cell definition, this field can be used to auto generate trend definitions (refer to Using Cells to Generate Trend Definitions for more information). This field cannot be changed once the cell definition is saved. Otherwise, this field is not used in I/NET Seven and can be any value.

Note: For manually defined trends, the cell number in the DCU editor does not need to match the cell number for the trend definition. The cell number in the trend definition is the one that will appear on reports.

  1. Select OK to save your changes. The system returns you to the Seven Trends Definitions window.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1823
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore