Using Event Sequence 0 to set default values for internal AO points

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Event Sequence 0 to set default values for internal AO points
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Tom_Poovey
    Tom_Poovey
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1295 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Event Sequence 0 to set default values for internal AO points

Picard Product_Support
‎2018-09-06 01:44 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-15 07:18 PM

Issue

Triggering a default value to internal AO points when the value is reset to 0

Product Line

TAC INET

Environment

  • I/NET Seven
  • Event Sequence 0

Cause

#A controller will run Event Sequence 0 any time one of these changes occurs:

  • Power up
  • Controller reset
  • Database restore

Internal AO point values will default to 0 (zero). If this AO point is used as a setpoint in a DDC loop, this could cause issues.

Resolution

Option 1

Use Event Sequence 0 to set internal setpoint values to a default value following power loss, reset, or restore.

  1. When connected to the controller, navigate to Edit > Controller > Event Sequences
  2. Click on Seq 0 and choose "Add." Sequence 0 is reserved to run on reset.
  3. Add an action
    • Action: Output (or Output with lock)
    • Delay: Defaults to 0
    • Point: AO that is used for the setpoint
    • Skip/Value: Desired default setpoint value.

Below is an example of what an Event Sequence 0 looks like of an Internal AO used as a setpoint. In this example anytime Event Sequence 0 runs, it will output a value of  75 degrees.

eventsequence0.png


Option 2

  1. Open up Event Sequences.
  2. Add event 0 to the list. Event sequence number 0 runs at a power up, after a reset of controller power or a database restore of the DCU.

    step1.png

  3. Modify event sequence 0. Put every interanal "AO" setpoint in this event with a default value that is safe to operate at. 

    step2.png

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5434
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore