Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

User names and passwords configured on a StruxureWare Building Operation Domain are not accepted by the AS's.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • User names and passwords configured on a StruxureWare Building Operation Domain are not accepted by the AS's.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • RobertAndriolo
    RobertAndriolo
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1787 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

User names and passwords configured on a StruxureWare Building Operation Domain are not accepted by the AS's.

Picard Product_Support
‎2018-09-11 04:23 AM

Issue

User names and passwords are not accepted by the AS's.

Environment

Domain

Password

Users

Cause

A new Domain was configured on the ES, this configuration was then exported, the export was then imported to each AS.

Resolution

Note;-

  • By importing and exporting copies of the Domain, Domains that are not related to each other, are created, which is unlikely to be the operational intent.
  • Exporting/Importing will duplicate user accounts etc. Having multiple accounts with the same name (potentially with different passwords) throughout the system can lead to an overly complex and un-manageable configuration.

To create a new Domain configuration, carry out the following.

  • Add the Automation Servers (AS) to the Enterprise Server (ES) in the normal way.
  • With the Workstation connected to the ES, select "Control Panel" and "Domains"

 

 

  • "Add" a new Domain, giving it a suitable name, and then select the AS's that will share this Domain with the ES.

 

 

 

  • Now Create the Domain.
  • At this stage, if the AS's are reviewed, the New Domain can be seen, (Note - Nothing is shown in the Domain folder on an AS).

 

                     

 

  • If required, you can choose to set the new Domain as the default Domain,  this is achieved by right-hand mouse clicking on the Domain and selecting the option. This must be done on each Server.

 

                                 

 

  • Confirm that the ES IP address is correct in all servers.

 

 

  • Finally create the User Groups, Users, and Workspaces required for this Domain.
  • Log off the Workstation, and restart  the ES.
  • Once the ES has restarted, log back on using the new Domain information.

 

  • Log on to an AS using the new Domain information.

 

  

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 13651
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of