Upgrading a BAS NIU Type 3 to a Sigma DNN – Location of Communications Cards
  • Upgrading a BAS NIU Type 3 to a Sigma DNN – Location of Communications Cards
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-06 12:56 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-21 12:29 AM
Clarification is needed on the physical location and port assignments of communications modules when upgrading a BAS NIU Type 3 to a Sigma DNN.
Satchwell BAS & Sigma
  • BAS NIU Type 3
  • Sigma DNN
  • Communications Modules (ARCnet, Ethernet)
There are three available module slots in the DNN (formerly NIU). Understanding how these slots correspond to port numbers is essential for proper network configuration.
Each module slot corresponds to a specific port number and network function:
  • Top Slot → Port 1
    • Typically used for Sub-LAN connections
    • Example: ARCnet module installed here
  • Middle Slot → Port 5
    • Typically used for Main Network connections
    • Example: Ethernet module installed here
  • Bottom Slot → Port 6
    • Typically used for Backup Network connections
    • Often left unused unless redundancy is required
Visual Reference:
In the image below, the DNN is configured with:
  • ARCnet in Port 1 (Top)
  • Ethernet in Port 5 (Middle)
  • Port 6 (Bottom) is vacant
  • Satchwell BAS & Sigma
Tags (2)
  • 6962
  • CraigEllis25