Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • Derrick_Ratliff
    Derrick_Ratliff
  • sesa194431
    sesa194431
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2929 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server

Picard Product_Support
‎2018-09-11 01:35 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-06 12:11 AM

Issue

Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server

Product Line

EcoStruxure Building Operation

Environment

  • WebReports
  • Reports Server
  • SQL Express

Cause

SQL Express 2008 R2 (for example) is limited to 10 Gb of Storage and 1 Gb of Ram usage. Many sites need a larger, more robust database than this allows.

Resolution

NOTICE: Before beginning, it is important to understand the difference between the Instance name and the version of SQL running.  The default instance name used in the the SQL Express version of SQL is SQLEXPRESS. This can be changed to anything during installation, but cannot be changed later.  This means that when upgrading to SQL Enterprise edition, the SQL instance name will still need to be SQLEXPRESS. The instruction below assumes the instance name is SQLEXPRESS and will be typed in that manner.  
  1. Perform a full backup of the Enterprise Server and Reports Server before beginning any upgrade process. Save these files to an external drive.
  2. Purchase a supported edition of SQL for the revision of EcoStruxure Building Operation WebReports being used. Please check the data sheet for the release to obtain this information.
  3. Open the Command Prompt and Browse to the location of the installation files for SQL. This should be the folder containing the setup.exe file for the new version of SQL
  4. Enter the Command "setup /ACTION=editionupgrade /INSTANCENAME=SQLEXPRESS /PID=XXXXX-XXXXX-XXXXX-XXXXX"
    NOTE:If  not using the default instance name, enter the correct instance name in place of SQLEXPRESS. PID is the product ID that came with the installation media. In some cases, this will be left out of the command string and entered later. (setup /ACTION=editionupgrade /INSTANCENAME=SQLEXPRESS)
  5. The SQL Installer will open. After the Setup Support Rules operation runs, click OK
  6. Click Next
  7. Verify the Product Key and click Next.
  8. Accept the License Agreement and click Next
  9. Ensure that the correct instance of SQL is selected and click Next.
  10. After the Edition Upgrade Rules runs, click Next
  11. Review the Upgrade Summary and click Upgrade
  12. When Complete click Close
  13. Open the SQL Server Configuration Manager using the start menu and verify that the SQL Server (SQLEXPRESS) service is running and that the SQL Server Reporting Services service is running. If either are stopped, right click and select the start option.
  14. Verify the upgrade is successful by opening a Web Browser and entering the URL "http://localhost/Reports_SQLEXPRESS" It should now be possible to see the option to directly edit reports in Report Builder.
  15. Log into the WebReports Interface. Notice that the initial report showing Database usage no longer runs.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 17145
  • ChrisAsbury22
  • DavidKendrick23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of