Upgrading SBO 1.x or EBO 2.x licenses to EBO 2022 v4 or later

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading SBO 1.x or EBO 2.x licenses to EBO 2022 v4 or later
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Gary
    Gary
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
8 Likes
15881 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading SBO 1.x or EBO 2.x licenses to EBO 2022 v4 or later

Gary Schneider Alumni (Retired)
‎2022-02-17 09:16 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2025-05-12 05:49 AM

Issue

Licenses required to upgrade SBO/EBO to EBO 2022 v4.0.x

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium - Secure boot
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Enterprise Server

Cause

Clarifying licensing upgrade requirements for EBO 2022 v4.0.x

Resolution

Example:

  • Upgrading a site SBO 1.x or EBO 2.x to EBO 2022 v4.0.x or later directly.
  • Site has an Enterprise Server (ES) the ES has 7x Automation servers AS-Ps and 2x AS-Bs attached.
  • One AS-P has a Modbus interface, and 1 AS-B has a Modbus interface.
  • Adding 1 additional AS-P classic (non-secure boot), 1x AS-P-S secure boot and 1 AS-B scalable.

The SBO 1.x or EBO 2.x licenses need to be upgraded to EBO 3.x first.

Upgrade ES licensing from SBO 1.x license to EBO 3.x. 
These licenses need to be activated using License Administrator.

 

  • 1 x SXWSWESUP13010 ES Upgrade from 1.X to 3.0 with 10 or less AS 

Note: Upgrading ES from 1.x gives the ability to host the maximum quantity of field devices / controllers at the Enterprise Server (600). Also, when a system is upgraded from 1.x, it will be provided with an unlimited (bounded by the maximums stated in the Architectural Guidelines) client license for connections to the Enterprise Server that has been upgraded.

 

The following additional licenses are required for each AS-x when upgrading a site from SBO 1.x to EBO 3.x or upgrading a site from EBO 2.x that was originally installed at SBO 1.x and upgraded to EBO 2.x.
These are not required if the site was originally installed at EBO 2.0 and upgrading to EBO 3.x.
These licenses need to be activated using License Administrator.

 

  • 7 x SXWSWASUP00001 license will be required one for each AS-P.
  • 2 x SXWSWASUP00001 licenses will be required one for each AS-B.

 

Note: If the site has more than 24 AS-xs then part number SXWSWASUP00099 provides 999 licenses.
EBO 3.2.x architectural guidelines allows a maximum of 250 AS-xs per ES.

 

Upgrade ES license from EBO 3 to EBO 4
This license needs to be activated using License Administrator.

 

  • 1 x SXWSWESUP30010 ES Upgrade from 3.X to EBO 2022 or later (i.e. to the current EBO version) with 10 or less AS


Upgrade AS-P/B licensing from EBO 3 to EBO 4 or later
These licenses need to be activated using Device Administrator.

 

For each AS-P (non secure boot AS-P and AS-P-NL), one of the following bundles would be required for each AS-P.

 

  • SXWSWASPUP30SA Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Standalone
  • SXWSWASPUP30SD Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Standard
  • SXWSWASPUP30EN Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle - Enhanced
  • SXWSWASPUP30FU Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Full
  • SXWSWASPUP30BP Full Bulk pack for upgrading AS-P-XX from EBO 3.x to EBO 2022 or later, contains 125 pieces of SXWSWASPUP30FU.
  • For the AS-P with the Modbus interface, an SXWSWX000MBRTU license is not needed as Modbus is grand-fathered for AS-P classics.

 

Note: Once an AS-P license is upgraded, there is no differentiation between AS-P Secure Boot and AS-P Non-Secure Boot (Classic):

 

If the “SXWSWASPUP30SD Upgrades an AS-P from EBO 3.x to EBO 2022 or later AS-P Bundle – Standard” license was purchased for an AS-P classic, and later it requires an enhanced or full license.

 

  • SXWSWXUP00SDEN ASP Bundle upgrade - Standard to Enhanced
  • SXWSWXUP00SDFU ASP Bundle upgrade - Standard to Full

Would need to be purchased.

 

If the “SXWSWASPUP30EN Upgrades an AS-P from EBO 3.x to EBO 2022 or later AS-P Bundle – Enhanced” license was purchased for an AS-P classic, and later it requires an  full license.

  • SXWSWXUP00ENFU ASP Bundle upgrade - Enhanced to Full

Would need to be purchased.

 

For the AS-Bs (AS-B-24, AS-B-24H, AS-B-36, and AS-B-36H), one of the following bundles would be required for each AS-B.
These licenses need to be activated using Device Administrator.

 

  • SXWSWASBUP30SD Upgrades AS-B from EBO 3.x to EBO 2022 or later AS-B Bundle – Standard
  • SXWSWASBUP30FU Upgrades AS-B from EBO 3.x to EBO 2022 or later AS-B Bundle - Full
  • A SXWSWX000MBRTU Modbus license is not needed with AS-Bs

Note: Once an AS-B license is upgraded, there is no differentiation between AS-B Scalable and AS-B (L) Non-Scalable (Classic):
If the “SXWSWASBUP30SD Upgrades AS-B from EBO 3.x to EBO 2022 AS-B Bundle – Standard” license was purchased for an AS-B (L) classic, and later it requires a full license.

 

SXWSWXBBUPSDFU ASB Bundle upgrade - Standard to Full, would need to be purchased.

 

To upgrade the AS-B-L (classic) type, the SXWSWASBUP30SD ASB Upgrade – Standard license is all that is required.

 

For the additional AS-P classic one of the following licenses would be required.

  • SXWSWASPUP30SA Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Standalone
  • SXWSWASPUP30SD Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Standard
  • SXWSWASPUP30EN Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle - Enhanced
  • SXWSWASPUP30FU Upgrades AS-P-XX from EBO 3.x to EBO 2022 or later AS-P Bundle – Full
  • For the AS-P with the Modbus interface, an SXWSWX000MBRTU license is not needed as Modbus is grand-fathered for AS-P classics.

 

For the additional AS-P secure boot one of the following licenses would be required.

  • SXWSWXBU0000SA ASP Bundle - Standalone 
  • SXWSWXBU0000SD ASP Bundle – Standard 
  • SXWSWXBU0000EN ASP Bundle – Enhanced 
  • SXWSWXBU0000FU ASP Bundle - Full 
  • For the AS-P secure boot if a Modbus interface is to be used the SXWSWX000MBRTU Modbus license would be required.

For the additional AS-B Scalable one of the following licenses would be required.

  • SXWSWXBBU010SD ASB Bundle – Standard
  • SXWSWXBBU050FU ASB Bundle – Full
  • A SXWSWX000MBRTU Modbus license is not needed with AS-B scalable.

If an additional AS-B classic was added one of the following licenses would be required.

  • SXWSWASBUP30SD Upgrades AS-B from EBO 3.x to EBO 2022 or later AS-B Bundle – Standard
  • SXWSWASBUP30FU Upgrades AS-B from EBO 3.x to EBO 2022 or later AS-B Bundle - Full
  • A SXWSWX000MBRTU Modbus license is not needed with AS-Bs

 

 

Addition:
If the site had an Enterprise Central (EC) at EBO 2.0 and was upgrading to EBO 2022 v4.0.x or later, one of the following licenses would be required to upgrade to EBO 3.x first:

 

  • SXWSWECUP23005 EC Upgrade with 5 or less ES
  • SXWSWECUP23010 EC Upgrade with 10 or less ES

Then one of the following licenses would be require to upgrade from EBO 3.x to EBO 2022 v4.0.x or later:

 

  • SXWSWECUP30005 EC Upgrade from 3.x - with 5 or less ES
  • SXWSWECUP30010 EC Upgrade from 3.x - with 10 or less ES

 

For more information on the bundles, search for 'software bundles" in the  “Part Numbers and Hardware/Software User Matrix – EBO 2024”

 

For information on software and features that require licenses

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • GaryMontague22
  • HernanUruena24
  • MahmoudSayed22
  • MahmoudSayed24
  • MahmoudSayed25
Was this article helpful? Yes No
95% helpful (17/18)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore