Upgrading Continuum from 1.5x to Continuum 1.9x

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading Continuum from 1.5x to Continuum 1.9x
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3164 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading Continuum from 1.5x to Continuum 1.9x

Picard Product_Support
‎2018-09-07 04:56 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:22 AM

Issue

What is the best way to upgrade Continuum Single User system from 1.5x to 1.9x?

Product Line

Andover Continuum

Environment

  • Continuum 1.5x, 1.5, V1.5
  • Continuum 1.6x, 1.6, V1.6
  • Continuum 1.9x, 1.9, V1.9
  • SQL Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Continuum Upgrade from older versions of Continuum.

Resolution

First upgrade to 1.74, then upgrade from 1.74 to 1.9x.   

PART I - Preparation:

  1. Acquire all software necessary to bring the workstations into compliance with 1.9x platform requirements.
  2. For each Cyberstation machine, make a record of the following
    1. Workstation name
    2. Folder name
    3. Device Node ID
    4. Network ID.
  3. From https://ecobuilding.schneider-electric.com
    1. Download Cyberstation 1.74
    2. Download Cyberstation 1.9x
  4. Download Microsoft SQL Server Management Studio Express
  5. Run Continuum Analyzer and resolve any issues.  An upgrade should not be done until the analyzer test report is clean.
  6. IMPORTANT - Make a backup of the Continuum database just prior to upgrading.

PART II - Upgrade Workstation 1 (Database server PC)

Uninstall 1.5x or 1.6x

  1. Shut down the Cyberstation applications on all workstations.
  2. Power down the workstations that are not running SQL and leave off until Part III
  3. Backup the contents of C:\Program Files\Continuum\UserProfile by copying contents to a flash drive or another folder.
  4. Backup the contents of the graphics file directory to a flash drive or another folder.
  5. Delete C:\Program Files\Continuum
  6. Uninstall SQL from Workstation 1 (DB server)

Install 1.74

  1. Install Continuum 1.74  (SQL 2000 SP4 will be installed automatically as part of the install)
  2. Run Database Initialization
  3. Create new database
  4. Initialize workstation using information from Part I.
  5. Launch Continuum to test that Cyberstation startup normally.
  6. Shut down Continuum
  7. Run Microsoft SQL Server Management Studio Express
  8. Navigate to ContinuumDB and Right Click
  9. Restore database backup from PART I
  10. Run Database Initialization.
  11. Update Continuum DB
  12. Update Workstation using information form Part I
  13. Launch continuum and verify that everything looks normal.
  14. Verify the integrity of the database by running Continuum Analyzer and correct any database issues before proceeding..
  15. Run Microsoft SQL Server Management Studio Express
  16. Navigate to ContinuumDB and Right Click
  17. Backup Database – name file so that it is clearly 1.74

Uninstall 1.74

  1. Uninstall Continuum
  2. Delete C:\Program Files\Continuum
  3. Uninstall SQL from Workstation 1

Install 1.9x

  1. Install all platform software necessary to bring the workstation into compliance with Continuum 1.9x requirements.
  2. Install Continuum 1.9x - (SQL Express will be installed automatically as part of the install)
  3. Run Continuum Database Initialization
  4. Create new database
  5. Update workstation with information from Part I.
  6. Launch Continuum to test that Cyberstation startup normally
  7. Shut down Continuum
  8. Run Microsoft SQL Server Management Studio Express
  9. Navigate to ContinuumDB and Right Click
  10. Restore 1.74 database backup.
  11. Run Continuum Database Initialization
  12. Update database
  13. Update workstation with information from Part I.
  14. Launch Continuum and verify that everything looks good.
  15. Run Continuum Analyzer and verify the integrity of the database.
  16. Backup Database

PART III - Upgrade Workstation 2 and 3

  1. Install all platform software necessary to bring the workstation into compliance with Continuum 1.9x requirements.
  2. Backup the contents of C:\Program Files\Continuum\UserProfile by copying contents to a flash drive or another folder.
  3. Uninstall Continuum from Workstation 
  4. Delete C:\Program Files\Continuum
  5. Install Continuum 1.9x
  6. Run DB Initialization and update database and workstation.
  7. Launch Continuum and verify that all looks well.
  8. Backup Database
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4474
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore