Update firmware warning in Menta when adding an I/O module to a Xenta 300/401

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Update firmware warning in Menta when adding an I/O module to a Xenta 300/401
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4314 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Update firmware warning in Menta when adding an I/O module to a Xenta 300/401

Picard Product_Support
‎2018-09-10 10:29 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:02 PM

Issue

When trying to add a Xenta 421A, 422A, 451A or 452A I/O module in Menta to a Xenta 300/401, the following warning is displayed.

Tam32
Warning, IO modules of type TAC Xenta 421A, 422A, 451A
and 452A requires at least system program version 3.6.

Environment

  • Menta
  • Vista
  • Xenta 301, 302, 401

Cause

To utilize the full functionality of the "A" series I/O modules, the version of Menta and firmware in the associated programmable controller must be compatible.

Resolution

Use the Xenta 4XXA modules as old 4XX modules
The I/O modules with an "A" in the name can be used with programmable controllers earlier than 3.61 as well as Menta earlier than 4.2.2 but the functionality will be limited. The functionality is limited to that of the modules' predecessors, modules without the letter "A" in the name (Xenta 421, 422, 451, 452). The TAC Xenta 421A/422A modules can only have digital inputs and the TAC Xenta 451A/452A modules can only have four 1.8k ohm thermistor and four limited universal inputs (digital input, 1.8k ohm thermistor or 0-10 V). In any running system with TAC Xenta 300/401 version 3.X, TAC Xenta 421, 422, 451, and 452 can be replaced with an "A" module the same way as an old module. The "A" module will detect that it is sitting in an old environment and behave as an old module.

Use the full functionality of the Xenta 4XXA modules
In order to gain full functionality of the "A" modules, the firmware in the Xenta 300/401 controller must be upgraded to a version 3.61 or higher and Menta must be version 4.2.2 or higher. Instructions on how to download a .MOT file can be found in Download an .MOT file into a Xenta Programmable controller. The additional features of these controllers include all inputs are universal inputs (0-10 V, 0-20 mA, 1.8k ohm and 10k ohm thermistor), universal inputs set as digital inputs can act as a pulse counter, and all configurations, inputs, and outputs can be accessed by means of the SNVT interface.

Note: If updating the firmware in a Xenta 300/401 and the following conditions apply than see the Xenta Programmables section of The new program interface does not match the previously defined program interface. (Subsystem: NS, #....

  • Working on a database with multiple Xenta programmable controllers that reference the same device template
  • A firmware version earlier than 3.52 is installed
Labels (1)
Labels:
  • TAC Vista
Tags (9)
  • Find more articles tagged with:
  • 10906
  • 3.6.
  • between
  • difference
  • information
  • least
  • requires
  • tam32
  • type
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore