Unifact Pro Controller – Averaging Network Temperature Across Master and Slave Controllers
  • Unifact Pro Controller – Averaging Network Temperature Across Master and Slave Controllers
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-11 06:13 AM
Last Updated: Administrator CraigEl Administrator ‎2025-10-07 03:26 PM
Temperature readings from two Unifact Pro controllers—each with its own sensor— are required to be averaged in the Sigma IC-Unifact system. The averaged value should then be transmitted back onto the network for use by both controllers.
Satchwell BAS & Sigma
  • Unifact Pro Master and Slave Controllers
  • Sigma IC-Unifact
  • Networked temperature sensors
Each Unifact Pro controller is equipped with a temperature sensor. When "Network Temperature Updates" is enabled:
  • The controller initially uses its local sensor value.
  • Upon receiving a network update, the local value is overwritten.
  • This overwritten value is then sent back to the Sigma IC, creating a feedback loop that excludes the actual sensor readings.
This configuration is not supported due to the feedback loop issue described above. Averaging temperature values across controllers using Sigma IC-Unifact will not work as intended because:
  • Controllers prioritize their own sensor data.
  • Network updates overwrite local values.
  • The overwritten values are re-sent, forming a loop that does not reflect true temperatures.
Consider alternative approaches such as:
  • Centralizing temperature averaging in a separate controller.
  • Using one controller as the master source of temperature data.
Additional Resources:
  • Sigma IC-Unifact Datasheet
  • Satchwell BAS & Sigma
Tags (2)
  • 14546
  • CraigEllis25