Unifact Pro Controller – Averaging Network Temperature Across Master and Slave Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unifact Pro Controller – Averaging Network Temperature Across Master and Slave Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2262 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unifact Pro Controller – Averaging Network Temperature Across Master and Slave Controllers

Picard Product_Support
‎2018-09-11 06:13 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-07 03:26 PM

Issue

Temperature readings from two Unifact Pro controllers—each with its own sensor— are required to be averaged in the Sigma IC-Unifact system. The averaged value should then be transmitted back onto the network for use by both controllers.

Product Line

Satchwell BAS & Sigma

Environment

  • Unifact Pro Master and Slave Controllers
  • Sigma IC-Unifact
  • Networked temperature sensors

Cause

Each Unifact Pro controller is equipped with a temperature sensor. When "Network Temperature Updates" is enabled:

  • The controller initially uses its local sensor value.
  • Upon receiving a network update, the local value is overwritten.
  • This overwritten value is then sent back to the Sigma IC, creating a feedback loop that excludes the actual sensor readings.

Resolution

This configuration is not supported due to the feedback loop issue described above. Averaging temperature values across controllers using Sigma IC-Unifact will not work as intended because:

  • Controllers prioritize their own sensor data.
  • Network updates overwrite local values.
  • The overwritten values are re-sent, forming a loop that does not reflect true temperatures.

Consider alternative approaches such as:

  • Centralizing temperature averaging in a separate controller.
  • Using one controller as the master source of temperature data.

Additional Resources:

  • Sigma IC-Unifact Datasheet
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (2)
  • Find more articles tagged with:
  • 14546
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore